Re: [RE-wrenches] Real info for voltage

2016-09-25 Thread Allan Sindelar
Bill, A true RMS meter shouldn't be necessary with a gennie in most cases, as the gennie is a rotating source, so the waveform is naturally true sine, or close. The true-RMS meter is more important with mod-square inverters, as cheap DMMs estimate RMS voltage as a proportion to peak voltage, a

[RE-wrenches] Real info for voltage

2016-09-25 Thread frenergy
Wrenches, I have a customer that is reading voltage with a non-RMS meter in the following scenario: 4000 watt Onan RV generator (older) at ~5500 foot elevation...its output is connected to the "AC in leg 1" of an OB VFX3648 using (customer installed, I came on this job after-th

Re: [RE-wrenches] Wireless AGS for Magnum?

2016-09-25 Thread John Blittersdorf
Ron, I have used a 12v adapter plugged into the 120 AC from the generator to the low voltage dc connection on the Magnum AGS unit to take care of the negative continuity problem. Then a wireless connection of the two wire start should work. On Thu, Sep 22, 2016 at 8:31 PM, RM You wrote: > H