DaveDid you make your MC Cables, are there any jumpers used, l have seen
crimped terminals cause faults and over time will overheat and fail open. Just
a thought.Jerry
Sent from my Verizon, Samsung Galaxy smartphone
Original message
From: Matthew Sirum
Lones,
Ok, so my question is if we save the original user settings to one SD card
and then format a separate SD card with the new firmware and install. Once
the new firmware is installed can we put the original SD card in and upload
all of our user settings. Or do we have to manually input all the
Hola Marco,
Advanced Energy was purchased by Beacon Power way back when, so you might
contact them to see if they have a manual. If you Google “Beacon Power M5
inverter” you can find a spec sheet, but I didn’t see the manual anywhere.
Brian
Brian Teitelbaum
Applications Engineer
AEE
Hola Wrenches,
I'm in search of a spec sheet and manual for a 2002 vintage Advanced Energy
Multi-Mode 5 kW inverter.
Looked on-line to no avail.
Please send to me off-line if you have these docs.
Mahalo,
marco
provision_highres_solar_logo2 with C-26351
Marco Mangelsdorf,
this might be unnecessary/ old school, but after i crimp i solder too
(oxidation happens).
todd
On Monday, November 14, 2016 1:16pm, "Ray Walters" said:
Here's the lug you would use for the inverter and batteries [
Here's the lug you would use for the inverter and batteries
https://www.delcity.net/store/Straight-Tinned-Copper-Lugs/p_810763.h_796015.t_1
It doesn't say here, but on the bag I got, it specifically is listed for
fine strand cables too.
I have 3 crimpers that I use: one like Allan's for the
Panduit ring tongue terminals and a Panduit full cycle ratcheting crimp tool.
Glenn
-Original Message-
From: "Will White"
Sent: 11/14/2016 12:34
To: "RE-wrenches"
Subject: [RE-wrenches] Ring Connectors
Hey Wrenches,
I'm
Will,
1/4" ring by whatever size wire you choose. Del City is a good source -
www.delcity.net. #153145 is 1/4"/#10AWG; #254145 is same for #8 and
#255145 for #6.
Standard indent crimper for non-insulated terminals, not the automotive
type. Mine is a Klein.
Allan
*Allan Sindelar*
Hey Wrenches,
I'm doing an upgrade to an Outback VFX series off-grid system with the
flexware boxes. What type/brand of ring connectors and crimpers do you all
use for the DC breakers with the post terminals?
Thanks,
Will
___
List sponsored by Redwood
Hello All
The legacy Mate(2) and legacy FX inverters did require the units to be sent
to OutBack to be updated.
The Mate3 and the FXRA inverters can all be updated in the field.
The newest revisions of software are available on the OutBack website.
Greetings Dave,
Have you considered possibly installing a hybrid type transient
voltage surge suppressor (TVSS), to include filters to remove high
frequency EMI/RFI? Or possible a straight line filter device? If
this nuisance arc fault issue is still occurring and it may be related
to an AC
You can use a Fluke 435 series, it will reveal any harmonics and record the
energy levels for each harmonic. It has a scope feature. You can rent one
pretty cheaply and record 24 hours of data. I can send you a sample report
from mine if you want.