Re: [RE-wrenches] SMA phantom arc faults

2019-09-02 Thread Jerry Shafer
Wrenches I have had chiller pump contactor along with wells, shop air compressors all create enough of an arc to trigger the inverters. ABB inverters only pick up off the DC but even there l had arc welders trip the inverters. Jerry On Mon, Sep 2, 2019, 8:14 AM frenergy wrote: > Interestingly,

Re: [RE-wrenches] SMA phantom arc faults

2019-09-02 Thread frenergy
Interestingly, the problems I've had with the SMA -40 AFCI faults have been on Comp roofs.  When I've gone "inside" a -40 with my laptop, I'm pretty sure I've seen where you can disable it? Bill On 9/2/2019 7:12 AM, drake.chamber...@redwoodalliance.org wrote: At least with the TL-22s, the

Re: [RE-wrenches] SMA phantom arc faults

2019-09-02 Thread drake . chamberlin
At least with the TL-22s, the AFCI function can be turned off. You need a_ Web connect speed wire module_. .I don't know if this same protocol will work for the TL 40s or not.  Metal roofing can apparently be affected by radio waves and by other factors that create a disturbance that can