Re: [RE-wrenches] Xantrex SW 4048 grid tie mystery

2019-12-22 Thread b...@midnitesolar.com
Forgot to say that if the inverters ARE grid tied, then they will NOT drift around in phase and will be synchronized  and therefore will stay in sync and be passing through from grid to output. boB On 12/22/2019 12:57 AM, Jerry Shafer wrote: Well l would start simple and get a sync

Re: [RE-wrenches] Xantrex SW 4048 grid tie mystery

2019-12-22 Thread b...@midnitesolar.com
You can test to see if both inverters are staying in sync by just watching the voltage between L1 and L2 of the outputs for a while.  If they do not deviate much from 240VAC over several minutes, then they are probably sync'd OK...  You can also help verify this by unplugging the sync

Re: [RE-wrenches] Xantrex SW 4048 grid tie mystery

2019-12-22 Thread Jerry Shafer
Well l would start simple and get a sync cable and make sure that they are al least staying g in correct phasing, then look closely at the programming, look at the grid voltages and settings, take it out of IEEE for test purposes only, you might find out you have a board that's out of calibration