Jay:
This idea sounds wrong on many levels. Generators are designed to be
loaded evenly, with some allowance for normal deviations. Having separate
loads that can vary independently is asking for regulation problems.
You did not state if the generator was wound Wye or Delta. This makes a
d
Drake, I have a TM 2025 I'd sell you for cheap. No shunt or 48v kit.
Contact me off list.
Dan Fink
Executive Director, Buckville Energy Consulting
NABCEP PV Associate
NABCEP Certified PV System Inspector
IREC Certified Instructor™ for:
~ PV Installation Professional
~ Small Wind Installer
NABCEP Re
Hi Jay
The FXR inverters do have the ability to run 2 legs of a 3phase system on a
single Mate3(s)and a Hub10.3
Inside the Hub10.3 is a header containing 5 jumpers. These jumpers can be
arranged so the inverters are set to a 3 phase
configuration.
Up to 9 inverters can be used per system, up to
Hi Dana,
That depends on the unit.
In my case its a large generator with large loads, the inverters being just one
of the loads. I can’t load one phase with 8kw, that would overload one phase.
Splitting the load to 2 phases, is within the capacity of the generator and
within the total loads