Code gurus,
It seems that a parking garage is properly considered to be a "building"
under NEC Article 100 definitions—and that 690.12 rapid shutdown
requirements would therefore apply.
I am wondering if anyone has successfully argued that 690.12 should *not*
apply to systems installed on the top
Wrenches
On the latest enphase issue withe fuses, swap leads L1 to L2 and to L1 and
wait if its the same fuse or same leg.
Jerry
On Thu, Aug 27, 2020, 4:29 PM Jason Szumlanski <
ja...@floridasolardesigngroup.com> wrote:
> So the resolution to this is in... But I still have no idea what was
> wron
Wrenches,
Huawei sent me a video link that displays their Bluetooth dongle as what looks
like a (optional) thumb drive which would emit the Bluetooth signal. I guess
now I know what that is.
This still did not resolve the issue of the intermittent connection when I
tried to connect my phone int
Hi Jason
One thought I have about the blowing fuse is to check it with a IR tool.
I suspect a poor connection of the fuse to holder which during higher air temp
is causing it to fail.
I’m assuming that the correct amp size and slow blow fuse Is installed and that
the wire connections are don
So the resolution to this is in... But I still have no idea what was wrong.
The string of 10 offending microinverters was split into 5 and 5. We had a
spare breaker in the IQ Combiner so it was relatively easy to run another
branch circuit. It has been over two months with no recurrence. So the
is
What about using an AC Coupled solution? The IEEE 1547 standard should only
be applied to the grid-tied inverter in that case since the hybrid inverter
is isolated when the grid is down and does not contribute to the grid sell
when the grid is up if there is no solar resource on the DC side (unless
Dave –
Related but different.
CA Rule 21 and HECO Rule 14H and NE-ISO require equipment tested to UL1741 SA
(which outlines what additional functions beyond UL1741 inverters must be
capable of) utilizing the appropriate utility Source Requirement Document
(SRD). The SRD spells out which UL 174
Wrenches,
Have any of you tried to connect to a Huawei SUN2000-45KTL (or similar) with a
smartphone via bluetooth? Using an iphone.
They say it requires a bluetooth dongle (phone usb charging cord) which, in my
mind isn’t “bluetooth” (which is wireless, isn’t it?)
Anyway, when I connect to the
Is IEEE 1547.1-2020 related to the issue in Hawaii (HEICO) too much
solar and cloud events that cause the transients? RULE 21 in California
kind of thing? Or, it it different please?
Dave Angelini Offgrid
Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
[1]
e-mail offg