Hi William,
Each Powerwall can accept 5 kW of continuous charge and 7 kW peak for 10
seconds. These values increase respectively with additional units (i.e.
10kW continuous for 2 units, 15kW for 3 etc). It’s my understanding that
each unit can accept 7.6 kW of AC coupled PV. If PV is generating mo
Max rating of the Gateway2 is 200A.
Regarding a generator input, you're correct, there's no means that I'm
aware of to integrate a backup generator with the Tesla equipment that
would interact with the solar and storage.
marco
On Thu, Apr 28, 2022 at 5:45 PM William Miller via RE-wrenches <
re-wr
Friends:
I have two questions about AC coupling Tesla systems:
1. Are there limits on how much power can be AC coupled through a Tesla
gateway? Does it depend on the quantity of power-walls connected?
2. I understand a Tesla system does not have a separate generator input
so if a genera
Chalk it up as another reason Rapid Shutdown is a bummer.
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
On 4/28/2022 9:11 AM, Harry Mahon via RE-wrenches wrote:
Dave – Unfortunately the SPS feature is not “back” fully.
Dave - Unfortunately the SPS feature is not "back" fully. Choosing "yes"
during commissioning for the SPS feature allows for it to work (with switch and
outlet installed) but ONLY for the same solar day as an outage occurs.
When the Sunny Boy goes to sleep, the sunspec transmitter will stop and
5 matches