Greetings Mac,
Have you personally had success with this by chance? I inherited
maintenance of a system for a friend whose original installer went out of
business and this was their original approach as well however they and they
had used the 100 amp version (even though the system produces just
William, thanks for the reply. In the scenario I'm thinking we use the Blue Seas
#3002 switch which has a battery bank A, bank B or A & B option.
Under normal circumstances he has it set to A When he wants to eq /
condition his Concorde PVX series AGM's he switches to bank A and begins
Hi,
There are several different ways to accomplish this via RF signalling.
One discussed before here is to use the IO-WRP kit from supplyhouse.com. I
did exactly what you want (disconnecting an inverter feed remotely when the
generator started) using this kit and relay / contactor.
And check
William and wrenches,
If these 24's are in there own conduit with no AC then it does not matter
as much but if the 24,s are in a blended conduitwith AC then your choice is
only AC and even then you may need a termination resistor to kill and
transient voltage at the contactor. Wires running
Hi William,
I don't want to hijack this thread but I want to give you another idea
for disconnecting the Enphase circuit.
Generac makes a very convenient load shed device called Smart Management
Module SMM50. This may be a good option for you. Instead of having a
signal wire/trench etc, it is
Friends:
I have an installation of 12 Enphase IQ inverters that is downstream from a
generator transfer switch. During power outages the generator will run
poorly when the Enphase is on and the sun is shining. The problems go away
when the Enphase is shut off. No surprises about this.
The