therefore by extension does not/can not had a GEC in the
system.
Exeltech (integrated micro-inverter aka. ACPV) does not seem to have a
lug on its chasis.
Has the industry pretty much moved to not requiring a GEC for these
devices and if so, how are the AHJ taking it?
Thanks,
Mark Frye
Berkeley
find materials with listing for the purpose but never got to the bottom
if it.
I have always had a problem when I saw thin wall AL flex being used with
twist-in-insert type fittings.
Mark Frye
On 11/9/2012 5:44 AM, Dave Click wrote:
Nick, what the AHJ is telling you may actually be in
Exactly,
Another fine example of how the Code works. Anyone out there have the
definition of "special permission".
Any changes have to go back to the NFPA? Really the buck stops at the
quasi-judicial authority of the head of the building department.
Inspectors are the bearers of that author
thoughts?
Mark Frye
Berkeley Solar Electric Systems
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
ded, but I can't find
references in the Code to support this.
Mark Frye
Berkeley Solar Electric Systems
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/opti
look at the size of the feeder breaker and the pv
breaker together to insure that the feeder has sufficient ampapacity per
690.49.
Mark Frye
On 6/5/2012 3:44 PM, Kirk Herander wrote:
Hello,
Ideally I'd like to make a supply-side tap on a feeder to a sub-panel.
And I mean tapping the fee
Not necessarily. NEC 2008, 250.32 (B), Exception allows you to use the
neutral conductor for existing structure so long as several requirements
are met.
Check it out.
On 4/11/2012 8:41 AM, Aladdin Solar wrote:
I meant the question largely to be a generic one but I can give you an
example:
Bur
Also,
Was a ground conductor run with the feeder?
Mark Frye
On 4/11/2012 7:09 AM, Aladdin Solar wrote:
Wrenches:
There's probably an obvious answer but please help me think this
through. Here's the situation--comes up all the time: The PV array and
grid-tied inverter will be lo
1 - What is the AC output rating of the PV inverter?
2 - What is the size of the feeder conductors?
3 - Does the sub panel at the garage have a main breaker of it's own?
4 - Does your AHJ or utility require anAC disconnect or not?
Mark Frye
Berkeley Solar Electric Systems
On 4/11/2012 7:
*
Rooftop solar installation sparks fires in Trenton, New Jersey*
28.03.2012: According to local news portal NJ.com, a rooftop solar
system has triggered several small fires at a recycling center in
Trenton, New Jersey. The article reports that "a major malfunction in
the rooftop solar pane
Still, if you put 2 x 4's on the ground between the batteries and the
floor, wouldn't the 2x4's have to be UL listed?
On 3/22/2012 3:53 PM, Brian Teitelbaum wrote:
Jeremy,
Sometimes the best "enclosure" is a locked room. Is it possible in
this case to wall off the space and provide a locked
Is there a Standard to which a battery enclosure can be tested such that
it can be listed and marked as conforming to the requirements of
performance that a battery enclosure must conform to in order for that
battery enclosure to be used as a battery enclosure?
Is the inspector looking at the
pling now available, do we yet know which is the more
advantagous architecture; grid-tied, battery-based inverter w/ PV on the DC
side via charge controllers, or grid-tied, battery-based inverter w/ PV AC
coupled via grid-tied, utility-based inverter?
Your thoughts?
Mark Frye
Berkeley Solar Ele
Folks,
How is the Enphase M215 doing? Is it showing marked improvements in
reliability over the previous generation units? Is the cable system going in
OK? I've worked with the M190 and M380 but not the M215?
Thanks,
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City
groups have succesfully integrated the
financial services into the product offering. 0$ down leases are now the
main offering.
This is a huge bar that the small shops can't even begin to touch.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401
Rich,
If you have an archive of Wrenches email, also see thread on this subject
dating on and about March 29, 2011.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
Fr
the Code makers? Why did they include the language
"capable of supplying multiple branch " if their intent was other than to
allow the use of dedicated load centers?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<
the service,
then the dedicated load center can be main lug without main breaker. If the
dedicated load center is located on a buidling remote from the the service,
then it will need a main breaker rated at 125A.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530
center for
things like monitoring equipment, it is reasonable that the above remain
unchanged so long as there is permanent marking stating that no additional
load circuits can be added (only supported by Code to the extent AHJ's can
make determination of acceptability.)
Mark Frye
Berkeley
apacity 2v cells, there is a size
range where a 24V system may in fact be the best choice.
Thanks and good luck with it out there.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
-Original Message-
From: re-wre
Polaris has the enitre grey fine stranded line of connectors.
Not sure if Burndy has connectors that are rated for fine stranded if that
is what you are using.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
-Original
o maintain...less watering, less SG measuring,
lower overall "part" (individual 2V cells) count?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
OK,
But let's assume only one string, how important is it to develop a higher
bulk charge current?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
-Original Message-
From: re-wrenches-boun...@lists.re-wrenche
AH
rating?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Tuesday, January
Todd,
I thought you were totally off-grid.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenche
Rebekah,
If you knew only the power and voltage, then you would use the root of 3 to
determine the amps. But since you know the amps, you don't need to use the
root.
The second equation would be the correct one.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City
eimbursement of
$150.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrench
Can you store the acid dry for ten years?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenche
I see. So there is a big difference between using the DC generator. With an
AC unit I can run it into the inverter/charger and it will give me three
stage charging. With the DC unit, I can really only us it to bulk charge.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City
How would you integrate a dc generator like to Polar Power into a "standard"
inverter/charge-battery-pv charge controller system?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.b
d no additional circuits."
I think this is a much better interpretation and method that preserves a
clean and functional load side connection topology. I think most reasonable
inspectors would agree as well.
Good Luck.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,
breaker in the
existing main panel. Move the existing 30A breaker into the new subpanel and
install the new 15A breaker into the same.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysol
er of the
frame brings it into square and on we go.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wr
electrode shall
be permitted to be used for both systems...
Review this article and share it with your inspector in order to determine
what is motivating him.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.
tting from Lumeta around this?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenche
be either a diversi9on
load or a contactor that disconnects the grid tied inverters all together.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
From: re-wrenche
Folks,
Has anyone talked with PG&E about needing (or not needing) a new
Interconnection Agreement when changing out inverter make and model without
increasing the size of the PV generator (number of modules) on a system that
is already interconnected?
Mark Frye
Berkeley Solar Electric Sys
, 75%? Would I have avoided most of my inverter failures
if I had?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mai
"Good" based on their online
configuration tool, and also well in line the the SMA white paper of many
years ago suggesting a 120% mod/inv ratio as optimal.
And yet, the first unit failed in 4 years and the refurb failed in 2 year.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud W
customers:
- Buy the refurbished units w/ 1 year warranty
- Buy new replacement units with 10 or 20 year warrranties
- Buy entirely new equipment such as Enphase or SolarEdge
What are other folks experiencing as we move well past the 5 year warranty
horizon for many of our earlier customers?
Mark Frye
f not, it is
possible that the coil taps are connected in a manner that is not efficient.
That being said, 15.6 A @ 120V sound like an awefully large number. Perhaps
you have a bad connection at one of your pull boxes.
I would be happy to stop by and take a look at the xfrm spec etc. with you.
ssing the
internal face gasket.
I really haven't looked into it much further but I wonder if the water you
observed entered through an incomplete connector mate, along the conductors,
into the inverter enclosure?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 9
Was that an M190?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On
dics meters.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Monday, Jun
The question is not well addressed without knowing the nominal dc system
voltage.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
From: re-wrenches-boun...@li
ure is
inherent in microinverters as well.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun
Thanks Phil,
I have already swapped the module to confim that the problem follows the
module, not the inverter.
I am currently working within channels with my distributor for warranty
replacement having just requested an RMA.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada
total
system yield
.0.0013%.
I am not complaining, just musing over this interesting evolution.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
___
List sponsored by Home Power magazine
, with high
voltage (over 250V) DC wiring, and doubling DC connector count.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
___
List sponsored by Home Power magazine
List Address: RE
How closely have you looked at this? It looks like the Tigo is already about
1/4 the cost of an Enphase. So how close are you to moving from an optimizer
/ inverter combination to a microinverter?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
Bob,
I think you are talking about Cougar Paws:
http://www.cougarpaws.com/
I love them and buy a pair for anyone who works for me.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysol
nd
upfront.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
of these three is electrically identical and
solidly connected inside the inverter. But, I don't know.
The folks at Enphase tech support will not tell me whether or not this is
true.
Anyone out there have any ideas about this?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada
..except..there wasn't any rubber there anymore...all rotted out.
Back in the day I went for a custom rolled cone flashings that I could caulk
into the post and slide a rubber counter-flashing over the whole thing.
Overkillperhaps.
Best of Luck.
Mark Frye
Berkeley Solar Electric Sy
Generally, in order to develope the full tensil strength of the bolt, it
should be engaged by a minimum of 5 threads.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
Folks,
I have a couple of new SunExtender AGM batteries that I will be using in a
UPS application.
My understanding is that I should cycle them before floating them out for
standby service.
Am I getting this right?
How many cycles - to what DOD?
Mark Frye
Berkeley Solar Electric Systems
303
hwest Technology Development Institute, New Mexico State University
575-646-6105 575-646-3841 (FAX)
http://www.nmsu.edu/~tdi/Photovoltaics/Codes-Stds/Codes-Stds.html
SWTDI/NMSU
3705 Research Drive
Box 30001/MSC 3 SOLAR
Las Cruces, NM 88003-8001"
Mark Frye
Berkeley Solar Electric Systems
Folks,
I did send the question to John Wiles and he was gracious enough to reply.
Here is his response:
"Mark:
Better ask the utility involved. Probably depends if they are on a common
transformer or not."
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,
it. Otherwise
it's onward and upward.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun.
Or another way to illustrate this problem:
There is nothing in the Code that would stop me from hauling out the old #6
and bonding my GEC to my next door neighbors GEC, if I wanted to?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<h
one of the two.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
I have not yet visited the site to see, but I would guess that they are feed
from the same transformer.
If they were, how would that make it OK?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.
ed systems in this case because each building
has it's own service and therefore cannot be considered as a seperately
derived system. So where does the Code speak to this.
My sense is that it is a big no-no, but can exactly explain why.
Anyone else out there agree or disagree?
Mark Frye
g the groundingstem of
multiple seperately derived systems, but could we construe a utility service
to one dwelling as a seperately derived system relative to another dwelling
with it's own service? Where can one find the definition of a "seperately
derived system" in the Code?
along my merry way?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] O
I have a customer who has two separate buildings, a home and a shop. Each
dwelling has it's own service.
He wants to put in two pv systems, one for each service, but wants all the
PV modules to be on the shop roof.
Why is mind going "clunk" when I try to deside if this is allowed
I see. Can this function be enabled/diabled?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenche
the DC diversion side
solution if you have someplace to put the power instead of just the
batteries, although that might be generally less commonly available for
retrofits into existing on-grid households.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401
ltage gets too
high. Once the voltage drops the contactor can close and bring the Fronius
back on line and then the 5-minute start up delay before it is feeding the
line again.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berk
caps using the gravity feed.
I don't have any idea what is going on with the distribution of the product
from Europe.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkel
a problem, so better safe than
sorry.
So now I see, I have to do what I have to do if I want to be even half as
good an electrican as my NABCEP certification says I am.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berk
C side of these inverters we
need more to concern ourselves with continuous overload conditions and not
so much with short-circuit/ground fault conditions?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar
fault from the
utility side of the equation far far exceed the currents contributed by the
power limited inverter side.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
F
over current
condition in any of that equipment.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenche
not exceed
the allowance for the feeder or the sub-panel. Still, if you do have loads
in the subpanel, you have to up sizes the sub-panel, but not the feeder
conductor.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.
Opps!
My bad, I was thinking of a single phase system, not the three phase system
shown in the article.
For the three phase system Kent is correct in counting 180A of supply per
bar.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<h
I think Kent and I agree. For the case where the subpanel is not dedicated a
PV sub-panel he is calculating for 2 - 50A breakers and I calculated for 3 -
50A breakers.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<h
ircuit, and above it, premise wiring.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wre
Ken,
In the situation you show in your drawing, what was the rating of the
transfer switch?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
From: re-wrenche
e 400A ATS will see the same 480A of supply breakers as the
conductors and busbar of the 400A load center. Here is where I am taking
leap of faith that the AHJ will agree with me that the same 120% allowance
given to the conductors and load center will be given to ATS itself.
Mark Frye
Berkeley Sola
t. Ulitmately my customer agreed with me that this was an undesirable
constraint on the operation of an otherwise reliable grid-tied system and it
was not clear that this would satify the warranty issue.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 9595
Can you send a link to one of these products?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re
) 519-1470
f: (604) 422-2756
Only have one of these puppies in the field, no problems yet.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re
ately derived system and would not require it's own system ground. At
that point, would the AC side of the inverter still be considered a
separately derived system or would the need for system grounding go away?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
e that
we don't need the complexity in wiring?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org]
nergy disipators
DC power supplies
Standby generators
??
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On B
nce such
that a problem with current capacities would be a problem. It seems like the
frequency would be more of a problem for some devices.
Anyone have experience with deliberately adjusting generator frequency away
from 60 hertz as described above?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud
wings to address voltage faults if they
occur.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenche
their time faulting and
resetting during daily peaks.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lis
Aaron,
Can you give a bit more information? Is this a situation where the meter and
the main disconnect are located on the outside of the building, with a
feeder running to a load center in the garage? Does the utility at this
location require a external lockable disconnect?
Mark Frye
viewed in PHOTON's archive using the
following link:
http://www.photon-international.com/newsletter/document/37644.pdf
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysola
Thanks August,
NFPA says there are giving away a softcover copy of 2011 to folks who take a
years subscription to NECPLUS before February something.
Seems like a good value.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
Does anyone here have the 2011 Code available on CD in a searchable format?
Know where to get it?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
e
switch in the basement.
I assume that the fused disconnect is co-located in the basement with the
service equipment?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
F
Al,
Are the inverters located inside on the 8th floor with the MLP panel or are
they located on the roof?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
From: re-wr
doing to counteract
the propogation of this mis-information within the marketplace.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches
How do utilites go about adjusting the voltage at any given site? Adjustable
taps on the transformers on the poles? Do they have to go back to the
nearest sub-station? Re-arrange the distrubution of customers across
differenat areas of the grid.
I am in the dark here.
Mark Frye
Berkeley Solar
Thanks William,
I did see your update from the 14th, but it did not provide any conclusive
details.
I am wondering if anyone has gotten any info since then.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.
Has any information become available about this fire?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wr
I am pretty sure you can get it from Multi-Contact USA.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wr
101 - 200 of 299 matches