Re: [RE-wrenches] 3 stack Radian Problem

2019-09-03 Thread Jay
Hi William I suspect a problem inverter, not a comm issue. If removing #3 stops the problem, then I’d move the #3 inverter into #2 slot and see if the problem still exists. If yes then It might just be one of the power modules inside #3. Or could be the control stack. I had a single power

Re: [RE-wrenches] 3 stack Radian Problem

2019-09-03 Thread Jerry Shafer
William Sounds like the inverters are in search not on, have you changed the inverters to on instead of search. Have you considered a hard reset to factory. Also as a POE (process of elimination) I would turn off one of the slaves at a time, even switch over to a different master. I had a 16 kg

[RE-wrenches] 3 stack Radian Problem

2019-09-03 Thread William Miller
Friends: The message below never got posted to the Wrenches list. I don't know how the list works but sometimes there is a quite a delay. I am still in need of advice. The problem went away mysteriously and then came back. I can make the problem go away by unplugging the data cable to

[RE-wrenches] 3 stack Radian Problem

2019-09-03 Thread William Miller
Friends: We have a 3 stack Radian system installed about two years ago. The customer had some health issues and is just moving into the new home. Over the weekend the system started strobing the AC output. One or more of the inverters was clicking and buzzing. Tech support diagnosed a