Re: [RE-wrenches] 600V charge controller questions

2016-01-31 Thread Roy Rakobitsch
Allan, you could network multiple Morningstar 600v controllers for the output ampacity required (up to 4 controllers, ...yeah, I know they are expensive). Would you even need a transfer switch? Why not just wire Fronius IG and Morningstar controller inputs in parallel (with associated fuses and di

Re: [RE-wrenches] 600V charge controller questions

2016-01-31 Thread Ray Walters
We were called in on a system similar to this, and we ended up just installing an AC transfer switch. Normally the GT array sold back to the grid side of the system, but in an extended outage, the customer had the option to switch the connection to the back up load side (AC coupled) He was made

Re: [RE-wrenches] 600V charge controller questions

2016-01-30 Thread jay
HI Allan, I’ll let you do the AC or DC couple choice. However my suggestion if you do DC couple is to go Schneider for all. Then you will have an integrated DC couple package. Metering and control, they have new battery meter and full online capability. And one of the things I don’t like abo

[RE-wrenches] 600V charge controller questions

2016-01-30 Thread Allan Sindelar
Wrenches, I am serving as a consultant for a homeowner with an array of solar equipment that doesn't do what he wants, a common story. He wants independence in the event of an extended utility outage. To cut to the chase: He has one array of 3,100 watts feeding t