Re: [RE-wrenches] Feeding 160A 3PH to a 800A/800A Main Service

2013-06-17 Thread Kirk
The 120% rule applies to both commercial and residential from the 2008 code on. Kirk Herander VSE On Jun 17, 2013, at 2:58 PM, Allan Sindelar wrote: > Pekka, > I believe that the 120% rule is only for residential application. Unless it's > changed (and I don't do commercial any more, so I may

Re: [RE-wrenches] Feeding 160A 3PH to a 800A/800A Main Service

2013-06-17 Thread John Stimac
Laine Sent: Monday, June 17, 2013 10:34 To: re-wrenches@lists.re-wrenches.org Subject: [RE-wrenches] Feeding 160A 3PH to a 800A/800A Main Service Dear Fellow Wrenches, We have a small 50kW 120/208V commercial job with five 9kW 3PH inverters, each outputting max. 25A. We are landing those into a dedi

Re: [RE-wrenches] Feeding 160A 3PH to a 800A/800A Main Service

2013-06-17 Thread Allan Sindelar
Pekka, I believe that the 120% rule is only for residential application. Unless it's changed (and I don't do commercial any more, so I may be all wet here) you're limited to 100% on commercial applications. The assumption is that a commercial service may alr

Re: [RE-wrenches] Feeding 160A 3PH to a 800A/800A Main Service

2013-06-17 Thread Brian Mehalic
True, as mentioned 160 is not a standard size, but you also cannot use a smaller size for a load side connection, unless you can use/find equipment rated for continuous duty...then you'd only need a 125A OCPD. Typos courtesy of my iPhone. On Jun 17, 2013, at 1:33 PM, Pekka Laine wrote: > Dea

Re: [RE-wrenches] Feeding 160A 3PH to a 800A/800A Main Service

2013-06-17 Thread Gary Willett
Pekka: 160A is not a "standard" OCPD value (NEC 2011; 240.6). I'd go with the next smaller size, or 150A. I would size the ampacity of the feeder conductors for 175A. Regards, Gary Willett Icarus Engineering On 6/17/13 12:33 PM, Pekka Laine wrote: Dear Fellow Wrenches, We have a small 50k

Re: [RE-wrenches] Feeding 160A 3PH to a 800A/800A Main Service

2013-06-17 Thread Max Balchowsky
a Laine To: re-wrenches@lists.re-wrenches.org Sent: Monday, June 17, 2013 10:33 AM Subject: [RE-wrenches] Feeding 160A 3PH to a 800A/800A Main Service Dear Fellow Wrenches, We have a small 50kW 120/208V commercial job with five 9kW 3PH inverters, each outputting max. 25A.  We are landing those i

[RE-wrenches] Feeding 160A 3PH to a 800A/800A Main Service

2013-06-17 Thread Pekka Laine
Dear Fellow Wrenches, We have a small 50kW 120/208V commercial job with five 9kW 3PH inverters, each outputting max. 25A. We are landing those into a dedicated load center with five 40A breakers. Doing the math, 5 x 25A x 1.25 = 156.25A, we would need a 160A breaker. This also equals to the m