> Wrenches,
>
> I have a client with a 4.6 kw grid tied system using a Sunny Boy 6000
> inverter. We have AC Coupled to that system with 2 Sunny Island 5048's and
> 8-Concorde SunXtender 3050T 6 volt batteries in series feeding an essential
> load/critical load sub panel. The wiring to th
Larry,
Would it not be better to connect the Honda directly to the the Sunny Islands?
Use a manual transfer switch to choose between the grid and the Honda. Then, in
an extended outage, your client could charge the batteries with it and turn the
darn thing off once in awhile. Maybe you could trans
Larry,
It sounds like the customer can power all loads with the generator and
the non-critical load may even be the motivation for starting the
generator? How about a relay that opens the SunnyBoy output or the Sunny
Island input when the generator runs?
Kent Osterberg
Blue Mountain Solar, I
the main SI tech guy for SMA America is Roy Dyngen. Let us
know what they say.
Jeffrey Quackenbush
NABCEP Certified PV Installer
Peripatetic Solar Technician
From: Larry Brown
To: RE-wrenches
Sent: Saturday, February 18, 2012 9:03 AM
Subject: [RE-wrenc
4 matches