...@asis.com To: RE-wrenches re-wrenches@lists.re-wrenches.org Sent: Wed, September 15, 2010 4:48:22 PM Subject: Re: [RE-wrenches] GEC for Enphase inverters Hi Nick, Last time I checked Evergreen modules don't work with positive ground systems. jay peltz power On Sep 15, 2010, at 9:19 AM, Nick

Re: [RE-wrenches] GEC for Enphase inverters

2010-09-16 Thread Dave Click
I'd worry about putting such a high current in anyway- Enphase's max input is 10A (max Isc 12A) while the Evergreen Imp is 11.69 for their 215W. Original Message Subject: Re: [RE-wrenches] GEC for Enphase inverters From: Nick Soleil nicksoleilso...@yahoo.com To: RE-wrenches re

Re: [RE-wrenches] GEC for Enphase inverters

2010-09-16 Thread jay peltz
Isc 12A) while the Evergreen Imp is 11.69 for their 215W. Original Message Subject: Re: [RE-wrenches] GEC for Enphase inverters From: Nick Soleil nicksoleilso...@yahoo.com To: RE-wrenches re-wrenches@lists.re-wrenches.org Date: 2010/9/16 10:58 Thanks Jay: That is true

Re: [RE-wrenches] GEC for Enphase inverters

2010-09-15 Thread Brian Mehalic
According to the Enphase website (/support/faqs): The Enphase Microinverter manual states that the device is positively grounded. Don't most PV modules have negative grounds? Is this a problem for Enphase? Enphase made the decision to positively ground its microinverters to minimize corrosion.

Re: [RE-wrenches] GEC for Enphase inverters

2010-09-15 Thread Nick Soleil
From: Brian Mehalic br...@solarenergy.org To: RE-wrenches re-wrenches@lists.re-wrenches.org Sent: Wed, September 15, 2010 6:19:21 AM Subject: Re: [RE-wrenches] GEC for Enphase inverters According to the Enphase website (/support/faqs): The Enphase Microinverter

Re: [RE-wrenches] GEC for Enphase inverters

2010-09-15 Thread Richard L Ratico
Brian, A GEC with no splices, or only irreversable splices, has only two ends. If you need to find them to check their integrity, you know where to look. No argument about acorn clamps. Exothermic welding might someday be required. Dick Ratico Solarwind Electric --- You wrote: Inspectors in

Re: [RE-wrenches] GEC for Enphase inverters

2010-09-15 Thread jay peltz
Hi Nick, Last time I checked Evergreen modules don't work with positive ground systems. jay peltz power On Sep 15, 2010, at 9:19 AM, Nick Soleil wrote: Yes, Enphase bonds the DC positive to ground in their inverters. This allows them to work with all modules, including SunPower. Nick

Re: [RE-wrenches] GEC for Enphase inverters

2010-09-14 Thread Kirk Herander, VSE
Installer VT Solar Incentive Program Partner _ From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller Sent: Tuesday, September 14, 2010 12:46 AM To: RE-wrenches Subject: [RE-wrenches] GEC for Enphase inverters Friends

Re: [RE-wrenches] GEC for Enphase inverters

2010-09-14 Thread Mark Frye
...@lists.re-wrenches.org] On Behalf Of William Miller Sent: Monday, September 13, 2010 9:46 PM To: RE-wrenches Subject: [RE-wrenches] GEC for Enphase inverters Friends: According to the 2005 NEC 250.64(C), the GEC for an AC system needs to be continuous without splices unless they are irreversible

Re: [RE-wrenches] GEC for Enphase inverters

2010-09-14 Thread Rebekah Hren
ma...@berkeleysolar.com wrote: From: Mark Frye ma...@berkeleysolar.com Subject: Re: [RE-wrenches] GEC for Enphase inverters To: 'RE-wrenches' re-wrenches@lists.re-wrenches.org Date: Tuesday, September 14, 2010, 10:05 AM I believe the AC GEC runs from; the point where the ungrounded current

Re: [RE-wrenches] GEC for Enphase inverters

2010-09-14 Thread Aladdin Solar
: [RE-wrenches] GEC for Enphase inverters The code does require the GEC to be continuous (250.64C), and I believe that the AC EGC for the Enphase metal inverter cases is in fact the same as the DC GEC since the point of system bonding on the DC side is inside the inverter. See art

Re: [RE-wrenches] GEC for Enphase inverters

2010-09-14 Thread Mark Frye
://www.berkeleysolar.com/ www.berkeleysolar.com _ From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Brooks Sent: Tuesday, September 14, 2010 8:41 AM To: 'RE-wrenches' Subject: Re: [RE-wrenches] GEC for Enphase inverters Mark

Re: [RE-wrenches] GEC for Enphase inverters

2010-09-14 Thread August Goers
] *On Behalf Of *Rebekah Hren *Sent:* Tuesday, September 14, 2010 7:25 AM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] GEC for Enphase inverters The code does require the GEC to be continuous (250.64C), and I believe that the AC EGC for the Enphase metal inverter cases is in fact the same

Re: [RE-wrenches] GEC for Enphase inverters

2010-09-14 Thread R Ray Walters
It seems to me that William's original question of where does the EGC stop, and the GEC begin, all depends on whether the Enphase inverters bond negative to ground internally. Did we ever get an answer from Enphase? If they don't, then I think by definition in article 100, we would only have an