Re: [RE-wrenches] GFDI requirements

2020-10-27 Thread Bradley Bassett
At least when we sold these they were not listed. We got caught on this a couple of times in WA state and were not allowed to install them. Also Grundfos said not to use a Gfi with them. Maybe a dc gfi might be ok on the PV side of the CU200. Brad Sent from my iPhone > On Oct 27, 2020, at

Re: [RE-wrenches] GFDI requirements

2020-10-27 Thread Dave Angelini Offgrid Solar
If it is all Grundfos electronics and the panels they specify, then I would get a permit and let the inspector make the decision. Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ [1] e-mail offgridso...@sti.net [2] text 209 813 0060 On Tue, 27

Re: [RE-wrenches] GFDI requirements

2020-10-27 Thread Brian Mehalic
Well Jay, if you call each of those poles "arrays" then you've got a path around the 2 parallel circuit maximum :) Note 2020 NEC language has changed a bit, though it's still not crystal clear: "PV system dc circuits that exceed 30 volts or 8 amperes shall be provided with dc ground-fault

[RE-wrenches] GFDI requirements

2020-10-27 Thread jay
HI All, I’ve got a question about GFDI requirements and do they apply to the following. Here is the project. 1. water pumping DC direct grundfos SQFLex 2. no humans anywhere around 3. no buildings or living structures 4. would be 3 pole mounts: each mount as 1 string, so 3 strings. 2019