--- On Thu, 4/23/09, Bob-O Schultze wrote:
> From: Bob-O Schultze
> Subject: Re: [RE-wrenches] Long MC Cable Mid String
> To: "RE-wrenches"
> Date: Thursday, April 23, 2009, 9:36 AM
> Nick,
> Oh yeah, the Electricalc Pro is the bomb. A new installer
> gets the logo T-
William,
That is exactly what I said in the first response to this thread,
(quote)"You should calculate your voltage drop for the entire round
trip distance of this circuit and size the wire accordingly. It does
not matter where the wire is located in the series circuit, just the
total le
Nick,
Oh yeah, the Electricalc Pro is the bomb. A new installer gets the
logo T-shirts, safety glasses, and one of those. I also recommend them
to my SEI students AFTER we teach the longhand version
Bob-O
On Apr 23, 2009, at 6:47 AM, Nicholas Ponzio wrote:
Dana,
I'm glad to hear that
Dana,
I'm glad to hear that you're happy with that calculator. I've considered
buying it in the past but I just couldn't get past the fact that the
website claims:
Enter BTU to find Kilowatts per Hour ...
-Nik
Dana wrote:
Voltage drop and Vd%
We have been using a Calculated Industrie
Friends:
We are missing some information. We know the mid-string distance, but what
is the distance from the positive and negative ends of the strings to the
inverter? This is all part of the entire string circuit and must be analyzed.
We have spent a lot of time researching voltage drop.
:
> From: Drake Chamberlin
> Subject: Re: [RE-wrenches] Long MC Cable Mid String
> To: dk...@aeesolar.com, "RE-wrenches"
> Date: Wednesday, April 22, 2009, 9:15 AM
> I have scratched my head on this one before, because it
> seems that
> two terminals bonded together by a
-wrenches.org] On Behalf Of Drake
Chamberlin
Sent: Wednesday, April 22, 2009 7:15 AM
To: dk...@aeesolar.com; RE-wrenches
Subject: Re: [RE-wrenches] Long MC Cable Mid String
I have scratched my head on this one before, because it seems that two
terminals bonded together by a wire are essentially the
boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Drake
Chamberlin
Sent: Wednesday, April 22, 2009 8:15 AM
To: dk...@aeesolar.com; RE-wrenches
Subject: Re: [RE-wrenches] Long MC Cable Mid String
I have scratched my head on this one before, because it seems that
(just to add another Dave to the thread)
Original Message --------
Subject: Re: [RE-wrenches] Long MC Cable Mid String
From: Drake Chamberlin
To: dk...@aeesolar.com, RE-wrenches
Date: 2009/04/22 10:15
I have scratched my head on this one before, because it seems that two
terminals
lin
To: dk...@aeesolar.com ; RE-wrenches
Sent: Wednesday, April 22, 2009 7:15 AM
Subject: Re: [RE-wrenches] Long MC Cable Mid String
I have scratched my head on this one before, because it seems that two
terminals bonded together by a wire are essentially the same terminal. The
th
I have scratched my head on this one before, because it seems that
two terminals bonded together by a wire are essentially the same
terminal. The theoretical voltage difference on a terminal is
zero. How do we figure a voltage drop on a wire that has near zero
volt potential between the ends
David,
There will be less than a 1 volt drop in 36 feet of 10 AWG at the 11
amps you get from the Evergreen modules. I don't think anyone will notice.
David
David Katz
David Palumbo wrote:
Does the following series string wiring cause a problem? With (18)
Evergreen ES-A 205's (low volta
Hi Dave,
You should calculate your voltage drop for the entire round trip
distance of this circuit and size the wire accordingly. It does not
matter where the wire is located in the series circuit; just the total
length.
Kindest Regards,
Larry Crutcher
Starlight Solar
(928) 941-1660
Rene
Does the following series string wiring cause a problem? With (18)
Evergreen ES-A 205's (low voltage modules 18.4Vmp) in series feeding a grid
tie inverter with a long series connector in the middle of the string. (2)
Top Of Pole 9 module mounts with the series connection from module #8 on the
fi
14 matches