Re: [RE-wrenches] Outback EQ not holding voltage

2020-04-30 Thread Dave Tedeyan
Howie, The timer does not reset when voltage dips below EQ, it just stops counting. So sometimes after 3 hours of EQ, the timer may have only counted down 30 minutes. Jay, I did try lowering the EQ voltage. When it was set to 62V, the voltage would hover at 62.0 and 61.9, then when it was lowered

Re: [RE-wrenches] Outback EQ not holding voltage

2020-04-28 Thread jay
Hi Dave, Only thing I would check is to see if lowering the eq by 1 volt changes anything. IE the batteries are just struggling to keep up. But the CC should tell you what mode it’s in right? IE is it regulating or is it full power. Either in the menus or just looking at VMP/watts If it’s

Re: [RE-wrenches] Outback EQ not holding voltage

2020-04-28 Thread Lones Tuss
? Sorry but nothing jumps out at me. Someone mentioned specific gravity. Are the SG readings widely separated? From: RE-wrenches On Behalf Of Dave Tedeyan Sent: Tuesday, April 28, 2020 8:17 AM To: offgridso...@sti.net; RE-wrenches Subject: Re: [RE-wrenches] Outback EQ not holding voltage Brian, I

Re: [RE-wrenches] Outback EQ not holding voltage

2020-04-28 Thread Howie Michaelson
I would tend to agree with Ray's analysis, with one question: - Does the Eq timer reset to 0 when the voltage dips? It should basically hold the time the batteries were at Eq voltage when it drops below, sort of putting the EQ timer on hold until the voltage comes back up. So

Re: [RE-wrenches] Outback EQ not holding voltage

2020-04-28 Thread Ray
I would add to the chorus that it probably is a battery issue. Here are the symptoms that lead to that conclusion: A) it started occurring recently, B) it is somewhat intermittent, C) the system has aging L 16s  (failures at 4 to 5 years are pretty  common) D) they are the Trojan RE series 

Re: [RE-wrenches] Outback EQ not holding voltage

2020-04-28 Thread Dave Tedeyan
Steve and Jerry, Thanks for the suggestions. I'll have to take a closer look at the battery bank next time I am out there. The solar setup is 4 strings of 3 kyocera 270's into each charge controller. So that is almost 65A @50V coming out of each charge controller for bulk. The parallel battery

Re: [RE-wrenches] Outback EQ not holding voltage

2020-04-28 Thread Steve Higgins
I know the old FX's didn't temp compensate in EQ mode but the charge controllers do... I know... that is what I said when I learned this years ago! I don't think the Radians observe temp compensation while in EQ either... That would be a better question for Lones Tuss... You out there Lones?

Re: [RE-wrenches] Outback EQ not holding voltage

2020-04-28 Thread Jerry Shafer
Sounds like a battery issue at first glance, as you EQ a battery it gets warm or even hot and this will effect ability to charge. If e en one of the L-16 is not exactly the same voltage you will not get to EQ untill another battery over voltages to show your overall volts. Need to look at each

Re: [RE-wrenches] Outback EQ not holding voltage

2020-04-28 Thread Dave Tedeyan
Brian, I had tried lowering the EQ voltage by 0.4V. The batteries still get up to the EQ voltage, but then fluctuate right at or 0.1V below. Dave, The EQ countdown timer does not count down when the battery voltage is below the EQ setpoint (even if by 0.1V). And since the timer never gets to 0,

Re: [RE-wrenches] Outback EQ not holding voltage

2020-04-28 Thread Dave Angelini Offgrid Solar
Does not sound right to me. Usually both Outback and Schneider protect against uncontrolled EQ time and end EQ. I think I would remove the network after the battery is full and test one controller at a time. Might have been damaged by lightning or gen glitching. Since you say it does this from

Re: [RE-wrenches] Outback EQ not holding voltage

2020-04-28 Thread Brian Mehalic
Sorry you had already answered the first two questions :) What about the others? Brian > On Apr 28, 2020, at 6:50 AM, Dave Tedeyan wrote: > >  > Hi All, > > I've got an outback system (Radian 8048A, 2 FM80, 16 Trojan L16RE-B) where > when the customer equalizes, the batteries hover right

Re: [RE-wrenches] Outback EQ not holding voltage

2020-04-28 Thread Brian Mehalic
What’s the capacity of the battery bank? And the size of the charging sources? What’s your EQ voltage? Have you tried a lower EQ voltage setting to see if it does the same thing? Brian > On Apr 28, 2020, at 6:50 AM, Dave Tedeyan wrote: > >  > Hi All, > > I've got an outback system (Radian

[RE-wrenches] Outback EQ not holding voltage

2020-04-28 Thread Dave Tedeyan
Hi All, I've got an outback system (Radian 8048A, 2 FM80, 16 Trojan L16RE-B) where when the customer equalizes, the batteries hover right around the EQ voltage, but will often dip to 0.1v less. Because of this, the EQ timer does not count down properly, and so left to its own devices the system