Young solarea...@solareagle.com wrote:
From: R Young solarea...@solareagle.com
Subject: Re: [RE-wrenches] Outback VFX input voltage cycling
To: Christopher Freitas cfrei...@outbackpower.com, RE-wrenches
re-wrenches@lists.re-wrenches.org
Date: Tuesday, December 30, 2008, 1:29 AM
Hi Chris,
My
little load.
If the same effect, measure the surge current to the inverter using
your meter. I think the surge should be very minimul.
Darryl
--- On Tue, 12/30/08, R Young solarea...@solareagle.com wrote:
From: R Young solarea...@solareagle.com
Subject: Re: [RE-wrenches] Outback VFX input
At 02:29 AM 12/30/2008, you wrote:
BUT ABOUT EVERY 20 SECONDS, JUST WHEN YOU WOULD EXPECT THE AC-IN TO
GET PICKED UP BY THE INVERTER THERE WOULD BE AN AUDIBLE CLICK, THE
VOLTAGE WOULD SUDDENLY DROP TO ABOUT 110V, THEN IMMEDIATELY RECOVER
TO ~121V. AT NO TIME DID THE AC-IN GET PICKED UP.
The
Hey Jay -
I have seen this type of problem before - but it was with Kohler
generators and the old SW series. They use a voltage regulation system
which actually increases the AC output voltage along with the AC load
level - they call it power boost and it is intended to offset the
voltage
...@lists.re-wrenches.org] On Behalf Of R Young
Sent: Sunday, December 28, 2008 8:51 PM
To: RE-wrenches
Subject: [RE-wrenches] Outback VFX input voltage cycling
This thread seems to have died ... somehow it got mixed in with the strings
of different orientation thread. If anyone has further input I would
, 2008 6:39 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Outback VFX input voltage cycling
I would also look at the loads. From an earlier post of yours it
appeared that the system ran more normally when not connected to the
house loads, but still cycled.
Could something on the load side
-wrenches
Subject: Re: [RE-wrenches] Outback VFX input voltage cycling
I would also look at the loads. From an earlier post of yours it
appeared that the system ran more normally when not connected to the
house loads, but still cycled.
Could something on the load side be shorting, or could
*Subject:* Re: [RE-wrenches] Outback VFX input voltage cycling
I would also look at the loads. From an earlier post of yours it appeared
that the system ran more normally when *not* connected to the house loads,
but still cycled.
Could something on the load side be shorting, or could
Hi Kirpal,
I understand and have sure seen lots of fixed generators that we not
fixed.
The guy who sells most of the generators I use used to be at Stanford
labs, smart guy.
I agree but I have never seen this type of problem, that is fixed by
turning on a few lights.
And to be clear,
Hi Chris,
My answers appear below:
On 29-Dec-08, at 10:41 AM, Christopher Freitas wrote:
When you tested just the inverter without the generator running –
you stated that there was a noticeable flicker every 20 seconds –
THE GENERATOR WAS RUNNING, IT'S JUST THAT I TURNED OFF ALL THE LOADS
This thread seems to have died ... somehow it got mixed in with the
strings of different orientation thread. If anyone has further
input I would very much appreciate it as I have to schedule a long
trip to remedy this and want to have as much ammunition as possible.
Again, to restate the
before the gen set
need attension, if not (changes to settings having occured or batteries just to
low) reduce the AC charge current.
Daryl
--- On Sat, 12/27/08, cvsol...@aol.com cvsol...@aol.com wrote:
From: cvsol...@aol.com cvsol...@aol.com
Subject: Re: [RE-wrenches] Outback VFX input
Hi Ron,
Almost for sure its the genny. What type and when was it last
serviced and how many hours does it have?
if the voltage is going all over the place really quickly then its not
connecting to the inverter at all.
So here is a test that might help. Turn on a resistive load such as
Ron wrote: The owner told me...that someone had wired a switch incorrectly
and when he turned it on the system shut down. He then re-wired it and
everything appeared ok but I'm wondering if this fried a board.
Mick replies: I've seen several times with Outback and other brands (going as
far back
Mick,
referring to
there's not an auto-idle switch on that genset which may have
accidentally been set for auto, is there?
His generator was actually running in idle mode, operating the
household loads when I got there and the first thing I discovered was
that the voltage was ~90 volts
I'm having a problem with an Outback VFX3524 inverter installed on an
E-panel in a remote off-grid location. Voltage at the inverter input
terminals is fluctuating between 110 140+ volts continuously. AC in
will not connect so batteries can't charge. Output voltage measured
at the
16 matches