Subject: Re: [RE-wrenches] Outback programing question
Hello Fellow Wrenches
Due to customer feedback OutBack decided to automatically enable the
Inverters Ac Charger if the Mate(3) called for an AGS (gen run) condition.
The general opinion here is if the gen is running you might
...@lists.re-wrenches.org] On Behalf
Of Darren Emmons
Sent: Friday, April 29, 2016 10:57 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Outback programing question
When the generator is auto started, the inverter's charger will be enabled.
After the generator is stopped, the inverter's ch
There's new firmware out today for the MATE3, you should probably try that.
On Wed, Apr 27, 2016 at 8:31 PM, jay wrote:
> HI All,
>
> I’ve got a problem that outback tech hasn’t been able to figure out.
>
> off grid system
> mate 3
> quad stacked VFX 3648
>
> The generator is set to specific sta
Why size is the generator?
How much load?
On Wed, Apr 27, 2016 at 8:31 PM, jay wrote:
> HI All,
>
> I’ve got a problem that outback tech hasn’t been able to figure out.
>
> off grid system
> mate 3
> quad stacked VFX 3648
>
> The generator is set to specific start/stop daily timer. This works f
That is what we are doing as a temporary fix.
According to outback the charger should stay off if it's set that way. It's
unclear why it's not doing it.
Actually opticsRE will allow full programming.
No phone app ( darn) but computer yes.
Jay
> On Apr 29, 2016, at 7:41 PM, Ray Walters w
Hi Jay;
Ah, its for load shedding. How come the max input amps setting doesn't
limit the total power drawn from the generator? That should throttle
back the charging rate to maintain full power thru to the loads.
Giving the batteries a 56 v for 5 min and dropping back to float
wouldn't const
Hi Ray,
I guess my answer is that its way easier to switch one button with easy access
than go deep into the menus and have to change 4 inverters.
This situation is a short term thing. In this case it is an issue as the
generator cannot handle both the chargers and the load. And he doesn’t wa
What's wrong with the chargers being on? Just set the charge settings
(absorb 56 v, and absorb time 5 minutes) fairly low. It will lightly
charge for a few minutes, and then go to float.
Just because your customer imagines this to be a problem, doesn't mean
it actually is. Its not going to hur
When the generator is auto started, the inverter's charger will be
enabled. After the generator is stopped, the inverter's charger will be
returned to the mode before the generator started. The logic is if you
are running the generator the Inverter's charger should be enabled. You
could lower t
Do you have the last firmware for the mate3?...002-019-000
Bill
Feather River Solar Electric
On 4/27/2016 5:31 PM, jay wrote:
HI All,
I’ve got a problem that outback tech hasn’t been able to figure out.
off grid system
mate 3
quad stacked VFX 3648
The generator is set to specific start/sto
HI All,
I’ve got a problem that outback tech hasn’t been able to figure out.
off grid system
mate 3
quad stacked VFX 3648
The generator is set to specific start/stop daily timer. This works fine.
The client has plenty of solar for the day, and when he runs his generator he
doesn’t want the ch