Follow up:
The charger on the Radian connected to the grid at 252 VAC today. It
appears that it is random when the inverter will connect. The AC grid
voltage does not appear to be the issue.
_Drake Chamberlin_
_Athens Electric LLC_
_Ohio Electrical Contractor's License 44810_
_NABCEP
What is the triggering for utility charge? % or volts or time of day or? I have seen this with offgrid generator use. It has to do with the rebulk volt setting being too low in relation to when the client started the generator. Their intial fix was to unhook the mate and plug it back in. That
It isn't in sell mode. The system is 2 or 3 years old, and has had this
issue before. Outback couldn't figure it out, and then is started
working normally.
---
_Drake Chamberlin_
_Athens Electric LLC_
_Ohio Electrical Contractor's License 44810_
_NABCEP Certified PV Installation
You could ask the wrenches bout how to make the window wider?
I don’t know
jay
> On Oct 31, 2023, at 10:14 AM, Jay wrote:
>
> Is the radian connected to grid sell?
>
> If so then I’d say yes the higher grid voltage is preventing connection.
>
> Jay
>
>> On Oct 31, 2023, at 9:35 AM,
Is the radian connected to grid sell? If so then I’d say yes the higher grid voltage is preventing connection. JayOn Oct 31, 2023, at 9:35 AM, Drake Chamberlin via RE-wrenches wrote:
Jay,
It was a problem that surfaced before. Outback tech support was unable to figure it out. Then, the problem
Jay,
It was a problem that surfaced before. Outback tech support was unable
to figure it out. Then, the problem went away. Recently it showed up
again.
For the last couple of days it has been connecting normally. The voltage
has been 250 VAC or lower.
I know that most direct grid tie
Drake I forgot to ask, but I’m thinking this is a new problem on an older system that was working normally?JayOn Oct 30, 2023, at 11:15 AM, david quattro via RE-wrenches wrote:I’m not familiar with Outback defaults but most inverters I’ve dealt with have a grid tolerance of 10% +/- so 216 to
I’m not familiar with Outback defaults but most inverters I’ve dealt with
have a grid tolerance of 10% +/- so 216 to 264VAC.
On Mon, Oct 30, 2023 at 6:57 AM Drake Chamberlin via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hi Jay,
>
> The inverter won't even connect to the grid.
Hi Jay,
The inverter won't even connect to the grid. It stays in the state where
it is sampling the grid, AC in light blinking.
Is the default high voltage for the nominal 240 V 280? (IE 140 V X 2).
Thanks for your help.
Drake
_Drake Chamberlin_
_Athens Electric LLC_
_Ohio
Hi drake
The early mate 3 has a glitch which I think they changed in the 3s.
You e got to set the rebulk volts above what you want it to charge at.
IE if the battery volts don’t get below the rebulk volts it won’t charge.
So if your shallow cycling the batteries it’s common it won’t get
My Radian GS 8048 intermittently will connect to the grid to charge
batteries. The grid voltage seems to run high around here. Yesterday, it
wouldn't connect. The grid voltage was at 251 V. Later it did connect.
At that point the grid was at 246 V.
I am suspecting that the Radian has a voltage
You can select which power module is used with the Mate under the inverter
settings. Left, right or auto. This way you won’t have to physically swap the
modules to determine if one has failed.
> Sent from a IPhone, with touch screen keys on the fly. Please excuse
> shortcuts and typos.
>
left (facing the box I assume)
> controls the one on the right. Tech support disappeared for the weekend
> before I could get any answers.
>
> Thank you,
>
> Drake
>
>
>
> - Original Message -
> From: "RE-wrenches"
> To:"RE-wrenches
uld work fine.
>
> Chris, at Outback, said the module on the left (facing the box I assume)
> controls the one on the right. Tech support disappeared for the weekend
> before I could get any answers.
>
> Thank you,
>
> Drake
>
>
>
> - Original Message ---
on the left (facing the box I
assume) controls the one on the right. Tech support disappeared for
the weekend before I could get any answers.
Thank you,
Drake
- Original Message -
From: "RE-wrenches"
To:"RE-wrenches"
Cc:
Sent:Sat, 4 Jan 2020 08:31:01 -0800
Subj
Hi Drake,
Yes on all accounts.
It can run on 1 as well.
Jay
Peltz power.
> On Jan 4, 2020, at 8:17 AM, drake.chamber...@redwoodalliance.org wrote:
>
>
> Hello Wrenches,
>
> Are the power modules in a Radian the same? Are the left and right ones
> interchangeable? What designates
Hello Wrenches,
Are the power modules in a Radian the same? Are the left and right
ones interchangeable? What designates the master as such? Is it the
ribbon cable connection to the control stack?
Thank you,
Drake
___