Hi Wrenches;
I have an upcoming project to be inspected, ,and having spent too much
time on off grid and out of country work, I'm now playing catch up with
the new 690.12 and 690.71(H) requirements.
The proposed GTB system is 3 Radians with a ground mounted 18kW array
and large HUP battery ban
I agree but how you shut it down is very different.
We can shut down BB inverter from the AC side as well.
Much easier, cheaper and does the same job.
my 2 cents.
jay
peltz power
> On Aug 26, 2015, at 4:41 PM, Tump wrote:
>
> Rapid shut down, should be the direction we as off/grid or on
HI Bill,
Thanks for your thoughts and clarifications on this super simple ( HA) topic.
But can you elaborate on the batteries are a potential massive bomb thing?
thanks
jay
peltz power
> On Aug 26, 2015, at 9:19 PM,
> wrote:
>
> Ray,
>
> Do you have a massive battery bank and 3, 8kW in
I know that IF the SMA SI master inverter is shut down then all follow, shunt
trip breaker only for the master? Also look at the Midnite MNBCB 1000/50
(Previous Model Num: MNBCB-1000/50-Battery Combiner)
MidNite 1000amp battery combiner box
Includes a 1000amp Positive and Negative bus bar with 3/
I spoke with Phil Undercuffler from Outback, who is a long term
respected member of our list (and nice guy). He basically said there is
a lot of misinformation on 690.12, but essentially it should only be
applied to roof mounted PV, and that it is specifically to address
firefighters' need to
Rapid shut down, should be the direction we as off/grid or on grid BB
installers should be moving towards. kinda like my flashing rant, we are in
the 21st century and we ARE professionals! We as an industry should be more
concerned about fire fighters and their safety BEFORE they goose step
Here's a link from the CO State Electrical Inspector Supervisor.
http://iaeimagazine.org/magazine/2015/01/22/rapid-shutdown-of-pv-systems/
Good article. Seems like off grid pole mount array and battery conductors WILL
apply.
Jeremy Rodriguez
Solar Installation And Design Expert
All Solar,
Hey I think Rapid shutdown is a cool idea too: you walk up and hit one
button and everything is safe. I've advocated for increased safety
including for batteries. But its at a cost: a big cost, especially for
small systems. While we debate what 690.12 applies to and which
equipment might wor
attery circuit to the inverter.
Bill.
-Original Message-
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
Behalf Of Ray Walters
Sent: Wednesday, August 26, 2015 12:40 PM
To: RE-wrenches
Subject: [RE-wrenches] Rapid Shutdown Battery Systems
Hi Wrenches;
I
nches.org] On
Behalf Of Ray Walters
Sent: Wednesday, August 26, 2015 12:40 PM
To: RE-wrenches
Subject: [RE-wrenches] Rapid Shutdown Battery Systems
Hi Wrenches;
I have an upcoming project to be inspected, ,and having spent too much time
on off grid and out of country work, I'm now play
turn off the battery circuit to the inverter.
>>
>> Bill.
>>
>>
>> -Original Message-
>> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
>> Behalf Of Ray Walters
>> Sent: Wednesday, August 26, 2015 12:40 PM
>> To: RE-