Good feedback. I'll note that we haven't seen any issues with the Eaton
60A, but we decided to go with Square D because it is robust and cost
effective.
Jason Szumlanski
Florida Solar Design Group
On Mon, Jan 3, 2022, 4:49 PM Dave Tedeyan wrote:
> Hi All,
> I thought I would follow up to
Hi All,
I thought I would follow up to report that I swapped out the old GE 60A
switch with a SQD one, and there have been no blown fuses since!
Cheers,
Dave
On Tue, Nov 2, 2021 at 4:50 PM Jerry Shafer
wrote:
> looks like one more failure, once they start there is no going back as the
> fuse
looks like one more failure, once they start there is no going back as the
fuse retainer loses its spring
On Tue, Nov 2, 2021 at 1:38 PM Jason Szumlanski <
ja...@floridasolardesigngroup.com> wrote:
> Ugh - no joke - we just found another one this morning with a blown fuse.
> Pic attached. It's
Trust me when I tell you that all of the line side conductors and taps are
likely fine. It is unequivocally the switch contacts that are the issue.
That said, I usually replace the conductors when there is any indication of
overheating near the terminals. I have seen discolored copper, but it
It is always the left fuse! Thanks all for the pointers. I'll double check
the monitoring, but am thinking that I will be replacing the switch with a
SQD, and replacing the taps and AC wires as well while I'm at it.
Cheers,
Dave
On Mon, Nov 1, 2021, 9:13 PM Jerry Shafer wrote:
> Bad switch
>
>
Bad switch
On Mon, Nov 1, 2021 at 5:44 PM Jason Szumlanski <
ja...@floridasolardesigngroup.com> wrote:
> See attached image. Notice the discoloration on the top of the left fuse.
> It's always the same thing, same place.
>
> Jason
>
> On Mon, Nov 1, 2021, 8:30 PM Jason Szumlanski <
>
I should also mention that it has nothing to do with ambient heat. This has
occured in all seasons and with disconnects in direct sunlight on a south
wall and disconnects in air conditioned garages.
It's just a garbage product. We switched to Square D for 60A D222NRB
fusible disconnects and are
It's the disconnect. We had dozens of this subpar disconnect design fail on
Enphase systems. The 2 Pole has the same issue.
GE gave us some nonsense answer that it's General Duty and not designed for
continuous high power. Even 40A combined Enphase systems will blow a 60A
fuse.
What you will
e to fail over time.
>>>
>>> We had a similar situation with a much larger system where the culprit
>>> was hard to notice…
>>>
>>>
>>>
>>> Best regards,
>>>
>>> Lloyd
>>>
>>>
>>>
>&
>>>
>>> We had a similar situation with a much larger system where the culprit
>>> was hard to notice…
>>>
>>>
>>>
>>> Best regards,
>>>
>>> Lloyd
>>>
>>>
>>>
>>> Lloyd H
>>> Lloyd
>>>
>>>
>>>
>>> Lloyd Hoffstatter
>>>
>>> Sunstruck Consulting
>>>
>>>
>>>
>>> Sent from Mail <https://go.microsoft.com/fwlink/?LinkId=550986> for
>>> Windows
>>>
>>&
;> was hard to notice…
>>
>>
>>
>> Best regards,
>>
>> Lloyd
>>
>>
>>
>> Lloyd Hoffstatter
>>
>> Sunstruck Consulting
>>
>>
>>
>> Sent from Mail <https://go.microsoft.com/fwlink/?LinkId=550986>
/fwlink/?LinkId=550986> for
> Windows
>
>
>
> *From: *Dave Tedeyan
> *Sent: *Monday, November 1, 2021 4:26 PM
> *To: *RE-wrenches
> *Subject: *[RE-wrenches] SolarEdge inverter blowing fuses
>
>
>
> Hi All,
>
>
>
> I am servicing a system that keep
HI Dave,
Which exact fuses do they have installed?
I’m guessing they are blowing due to not being constant load rated fuses and
summer higher temps.
jay
peltz power
> On Nov 1, 2021, at 2:26 PM, Dave Tedeyan wrote:
>
> Hi All,
>
> I am servicing a system that keeps blowing fuses on the
tps://go.microsoft.com/fwlink/?LinkId=550986> for Windows
From: Dave Tedeyan<mailto:d...@sungineersolar.com>
Sent: Monday, November 1, 2021 4:26 PM
To: RE-wrenches<mailto:re-wrenches@lists.re-wrenches.org>
Subject: [RE-wrenches] SolarEdge inverter blowing fuses
Hi All,
I am servicing a
Hi All,
I am servicing a system that keeps blowing fuses on the AC side, although it
appears that everything is sized correctly. It is a SolarEdge SE11400A-US
inverter.
Max continuous output current is 47.5A x 1.25 = 59.4A. There is a GE
TG3222R
60A AC disconnect, and it is wired up with #6