Re: [RE-wrenches] automatic transfer switches

2019-11-29 Thread Chris Mason
If you are doing it on the AC side, a Generac transfer switch has the capability and is designed to do this. It's easy to rig an interface as I discussed privately with Bill. On Fri, Nov 29, 2019 at 1:29 AM Jerry Shafer wrote: > Wrenches > Need to be careful here to use something that has the

Re: [RE-wrenches] automatic transfer switches

2019-11-28 Thread Jerry Shafer
Wrenches Need to be careful here to use something that has the interrupt KVA rating required to prevent an arc in the event of an under load opening with the switch proper AIC rating 10,000 or more, last thing I think you want is to have that kind of liability on products that are not designed for

Re: [RE-wrenches] automatic transfer switches

2019-11-26 Thread Chris Mason
If you only want to change over, why not use a contactor with three poles, a NO and NC contact? that will switch instantly. Use Utility to power the coil, it will switch to utility when the power is restored. On Tue, Nov 26, 2019 at 2:57 AM Jerry Shafer wrote: > There is the SMA Automatic

Re: [RE-wrenches] automatic transfer switches

2019-11-26 Thread Mac Lewis
Hi Bill, We just did something like this with a hydro plant and backup solar site. We ended up using a Kohler RDT transfer switch with the accessory board. With the accessory board, its possible to adjust down to about ~1 second transfer, and without the accessory board, its ~3 second transfer.

Re: [RE-wrenches] automatic transfer switches

2019-11-25 Thread Jerry Shafer
There is the SMA Automatic transfer switch if you go with the SMA battery inverter and SMA pv inverter, it can be located seperate of the battery and inverter and will take up to 30 kwhrs. of capacity Just a thought On Mon, Nov 25, 2019, 10:52 PM Bill Hennessy wrote: > hi folks-- > > We're

[RE-wrenches] automatic transfer switches

2019-11-25 Thread Bill Hennessy
hi folks-- We're installing a grid-tied, battery backup system on a farm where the service entrance is on a pole in the yard. At the single-phase, 240v, service entrance, there are two main breaker subpanels--one going to the house and one to the barn. The buildings are each about 100 feet away