I do vaguely recall this a few months ago on the forum and forget what we
came up with, so here's just my thoughts before breakfast ...
The standards do not specifically call out a requirement for nail plate or
protection of piping. However, depending on which codes are in effect at
the location
Thanks Chris and everybody, this is the information I was looking for.
Dewayne
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris
Cahill
Sent: Monday, February 15, 2010 6:05 PM
To:
We feel regardless of code, it is well worth the added protection. While it my
not stop a nail gun it will stop the random drywall screw and finishing nails.
Thanks,
Eric Tysinger CET
NICET 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p:
It will usually stop a drywall screw, until the drywall guy decides that he
absolutely needs a screw right there and uses a self taping screw. (This just
happened to us a couple of months ago.)
Daniel L. Merkle, CET
NICET # 118915
Automatic Sprinkler System Layout, Level III
COLONIAL Fire
Has any one come accrose 2 adajent buildings with one sprinkler
riser ? Is it allowed by NFPA 13 ? Your comments are highly
appreciated.
The contents of this email, including all related responses, files and
attachments transmitted with it (collectively referred to as this Email), are
It is allowed with some restrictions in 2007 NFPA 13, 8.2.4.
Richard Carr, SET
Design Manager
Associated Sprinkler Co., LLC
336.373.3901 ext 217
richa...@associatedsprinkler.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
The air flow over the surface impacts how quickly the link or car
heats up but not how hot it gets since that is a function of the
exposing temperature. We could dug up the old heat transfer equation
for convection but I don't think many really want to go that far.
Naturally there is an
http://www.freepatentsonline.com/4738314.html
As taken from the literature It has been found that fusible link elements
which are used to support loads in various devices and in particular in
automatic fire fighting equipment encounter load and stress variations due to
changes in temperature,
Does an air compressor for a pre-action system have to be wired on a
dedicated circuit?
The release panel?
Thanks,
Greg
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
It's a good idea if you need to service the compressor, but I don't think
it's required in NFPA 13. Maybe in the elec. Code.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Greg McGahan
Sent: Tuesday,
I did this a couple of years ago by direction of the AHJ - I didn't agree
with it but it saved the building owner a lead in and a double check
assembly. The project was an old college campus with two buildings
consisting of a total floor area less than 52,000 square feet, building A
had the main
Haji,
NFPA 13 does allow adjacent buildings to be served by a single riser but the
conditions are limited. The intent of the committee at the time this
proposal was accepted was to allow a cost effective means to get fire
protection to auxiliary buildings (like schools) or out buildings
In note 2 on table 12.2.3.1.6 (2002 - 13), they reference
nonexpanded, stable, solid unit load. What is meant by solid unit load?
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
___
Dear Forum Members,
I apologise for my ignorance on the subject in reference but I do have
two questions regarding the use of sprinklers that I am supposed to use for an
area classifies as ordinary risk II:
1. Could I use sprinklers recommended for LIGHT HAZARDS in areas classified
as
NFPA-13-2007 paragraph 3.9.2.7 I believe
Mike
Date: Tue, 16 Feb 2010 11:45:20 -0500
To: sprinklerforum@firesprinkler.org
From: t...@fpdc.com
Subject: solid unit load?
In note 2 on table 12.2.3.1.6 (2002 - 13), they reference
nonexpanded, stable, solid unit load. What is meant by
Cesar,
You will have to go by the listing for the sprinkler. If it is
specifically listed for Light Hazard only, you can't use it for OH.
If it is listed for use in NFPA 13 occupancies, it could be used in
Light or Ordinary. The Tyco RFII can be used in on OH occupancy, such
as a retail
Release panel is to be on a dedicated branch circuit per NFPA 72, 4.4.1.4
(2007), se also NFPA 70, 760.41 760.121.
Compressors, couldn't find anything specific in Electrical code or 13. Just
make sure there's a low pressure alarm (NFPA 13, 7.9.2.2) incase the compressor
is shut off or fails.
Missed that page. Thanks
At 11:59 AM 2/16/2010, you wrote:
NFPA-13-2007 paragraph 3.9.2.7 I believe
Mike
Date: Tue, 16 Feb 2010 11:45:20 -0500
To: sprinklerforum@firesprinkler.org
From: t...@fpdc.com
Subject: solid unit load?
In note 2 on table 12.2.3.1.6 (2002 - 13), they
Dear Todd,
Thanks for the quick reply.
Yes, you are right about where I am going to, I am planning to use Extended
Coverage Sprinklers - concealed type. What should I do?
Rgds,
Cesar Villavicencio
- Original Message
From: Todd Williams t...@fpdc.com
To:
Either go to standard spacing or semi-recessed heads.
Sent from my iPhone
Ron Greenman
...On the phone
On Feb 16, 2010, at 3:53 PM, Cesar Villavicencio cesarv...@yahoo.com
wrote:
Dear Todd,
Thanks for the quick reply.
Yes, you are right about where I am going to, I am planning to use
The carburetor of my Cessna 172 Skyhawk can accumulate ice at ambient
temperatures up to around 70 Deg F. There is a pressure drop in the throat
as a result of the venturi effect. This is why mounting main drain pressure
gauges on the 2 main drain itself will produce an inaccurate
residual