I presume you mean a window with two panes separated by a vertical mullion.
By most Codes/Rules: If the sprinkler/drencher is located centred on the
mullion then one is OK. If mullion is less then 40mm proud of surface it can
be ignored. Otherwise each pane of a window must be sprayed individually.
, 2013, at 7:34 AM, Greg McGahan wrote:
>
> > Waste of money
>
> -- next part --
> An HTML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130221/4118400a/attachment.html
&
ML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130221/69173d31/attachment.html
> >
> ___
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.or
I beg the Forum's pardon. I should know better than to post from home
(snow day in Kansas. I have a good memory, it's just short). I think
vertical mullions not being an obstruction makes sense though,
otherwise the listing would not distiguish?
Quoting Justin Reid :
IBC 2012, 703.4
Just
IBC 2012, 703.4
Justin Reid
Sent from my iPhone
On Feb 21, 2013, at 3:33 PM, "Cahill, Christopher" wrote:
> Not to be picky but IBC 2013? Don't ya mean '12? What section are you
> referring to that sprinkler rating equivalent changed? I can think of two
> areas that had rating tied to spr
Not to be picky but IBC 2013? Don't ya mean '12? What section are you
referring to that sprinkler rating equivalent changed? I can think of two
areas that had rating tied to sprinklers, atriums and substitute for 1 hour
construction. Did they change?
Chris Cahill, PE*
Senior Fire Protectio
I think only horizontal mullions are considered an obstruction to
wetting the glass. Also, in IBC 2013, the sprinkler equivalent for
Fire Rated is no longer approved.
Quoting Rod DiBona :
Pretty sure you do. The mullion acts as a barrier. More than likely
if you present the dilemma to the
Pretty sure you do. The mullion acts as a barrier. More than likely if you
present the dilemma to the A/E team they change the window.
Rod at Rapid
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva
I have two windows, each 2'-6" wide, separated by a vertical mullion. Do I
need two window sprinklers?
Tony
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
sprinkler.org/mailman/private/sprinklerforum/attachments/20130221/4118400a/attachment.html>
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
We have a two story strip mall with a Bank at one end. The Bank is currently
sprinklered, monitored and alarmed for water flow. The adjacent site (
Building?, location?, tenant?) is currently being sprinklered by others from
the same riser. Does this ( Building?, location?, tenant?) Requir
ML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130221/69173d31/attachment.html
> >
> ___
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball
tem and back out heads carefully with
> system under pressure and vent the air from those points.
-- next part --
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130221/69173d31/attach
15 matches
Mail list logo