Thanks for sharing this information.
My question is this: Tyco data sheets state locate window sprinklers within
each mullioned segment. Whereas it is not required for butt-jointed window
assemblies, provided the sprinkler spacing is maximum 8 feet. So clearly
they consider the mullion to be an
Personally I don't believe that requires ANY thought or hatred (some day I will
learn to type well enough to avoid such amusing typo's. At least you don't
make fun of my southern nnunciation).
Roland
On Feb 21, 2013, at 2:10 PM, Ron Greenman rongreen...@gmail.com wrote:
Interesting
://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130222/cf3ed2c9/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20130222/cf3ed2c9/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
--
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20130222/cf3ed2c9/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http
with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
-- next part -- An HTML attachment was
scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta
ch ments/20130222/cf3ed2c9/attachment.html
The Ames check is a threaded assembly designed for replacement, so listing
isn't an issue. And it could be coincidence that the half dozen times we've
corrected this by replacing the checks evacuated the air also, but if you
contact Ames you'll find they know about this happening.
I also think
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130222/f5a80b72
://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130222/f5a80b72/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
Well.. each mullioned section would mean vertical, since horizontal
are not allowed. This means the water has to run accross the glass,
not just down. I saw the width of it running down, regardless of
vertical mullions as the max horizontal spacing. I think a case for be
made for not