Re: [EXTERNAL] Re: Exterior Play Area

2018-04-13 Thread bcasterline
I say when it gets to 2550 kW, stand back about 5 feet with a six foot stick and toast some marshmallows Quoting "Mark.Phelps" : One of the issues considered for sprinklers or not is in the egress and exiting. In a freestanding building with no exterior walls, egress and especially exiting

Re: [EXTERNAL] Re: Exterior Play Area

2018-04-13 Thread Mark.Phelps
One of the issues considered for sprinklers or not is in the egress and exiting. In a freestanding building with no exterior walls, egress and especially exiting is not an issue and many jurisdictions specifically do not require sprinklers for this reason. Could this be the answer? What say y'a

Re: [EXTERNAL] Re: Exterior Play Area

2018-04-13 Thread John Irwin
Aww now you're going to make me pause Boss Baby and get my laptop. I should also note that there are "engineered FPs" with this set but give no direction on anything..  Florida engineering laws really need to change.. ⁣John Irwin  DynaFire Inc.  Tampa Fire Sprinkler Division  727-282-9243  This

Re: [EXTERNAL] Re: Exterior Play Area

2018-04-13 Thread Travis Mack
Is that considered a building? Check the architectural code study. That should say if the architect is half decent. If it defined as an exterior projection then follow the means to omit in NFPA 13. If the code study calls it a building, then you protect. It can’t be a projection if it is a bu

Re: [EXTERNAL] Re: Exterior Play Area

2018-04-13 Thread John Irwin
I spend nearly as much time in the Florida Building Code as I do NFPA 13. So riddle me this Batman (and I'm not saying you're wrong here) but here in Florida plenty of schools have covered play areas that are not attached to any building. Many are large enough for a full sized basketball court.

Re: [EXTERNAL] Re: Exterior Play Area

2018-04-13 Thread Travis Mack
As Steve pointed out, it is a building. That gets you to point of sprinklers. I guess this comes to a point of defining this structure as an exterior projection or a building. I agree with Steve and see it as a building as described. What I was getting at is we sprinkler people often search

RE: [EXTERNAL] Re: Exterior Play Area

2018-04-13 Thread Kyle.Montgomery
So, Travis, what is the “clear” answer in the building code? As far as I can tell, it’s still an exterior projection of noncombustible construction. Thus, the entire argument hinges on whether or not there will be combustibles stored beneath. I’ll allow for the argument that there could “potent

Re: Exterior Play Area

2018-04-13 Thread bcasterline
Travis, "I am he as you are he as you are me and we are all together" ~john lennon~ . Quoting Travis Mack : We need a LIKE button for emails. So many times people get lost debating NFPA 13 criteria when the answer is quite clear in the building code. Travis Mack, SET MFP Design, LLC "Fo

Re: Exterior Play Area

2018-04-13 Thread Travis Mack
We need a LIKE button for emails. So many times people get lost debating NFPA 13 criteria when the answer is quite clear in the building code. Travis Mack, SET MFP Design, LLC "Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to MFP Design via

Re: Mech room sans ceiling & full height walls

2018-04-13 Thread John Irwin
I've seen this. Never had too much trouble getting a ceiling added when I give them the add alternate for installing sprinklers at the roof. Checking wall heights is usually one of the first things I do when opening a fresh set of plans. Half a dozen different color highlighters and a cup of co

Re: [EXTERNAL] Re: Exterior Play Area

2018-04-13 Thread bcasterline
Actually, this is all i would do anyway, even if it was 40x50-- I'd call it "exposure protection" B Quoting bcasterl...@fsc-inc.com: I doubt this is a 20 ft wide by 100 foot projection John but if it was you could stub out ten or twelve light hazard dry sidewalls off the wet system inside

Mech room sans ceiling & full height walls

2018-04-13 Thread Ed Kramer
This is something we're seeing occasionally and I'm wondering if others are seeing it also. A typical office area within a noncombustible building. All rooms within the greater area have lowered finished ceilings, are mostly light hazard, and the space above is noncombustible and (almost) conc

Re: [EXTERNAL] Re: Exterior Play Area

2018-04-13 Thread bcasterline
I doubt this is a 20 ft wide by 100 foot projection John but if it was you could stub out ten or twelve light hazard dry sidewalls off the wet system inside -- 2-3 grand? to placate yourself, the ahj, and the lawyers if it all went south some day? ?B. Quoting John Irwin : Yeah I didn't thi

RE: [EXTERNAL] Re: Exterior Play Area

2018-04-13 Thread Kyle.Montgomery
In all seriousness… I think if it is noncombustible construction with no combustible storage underneath, then you should be OK to omit sprinklers. If it’s just a concrete basketball court, then I think that meets the criteria. That being said, I would leave open the possibility of an unfavorable

RE: [EXTERNAL] Re: Exterior Play Area

2018-04-13 Thread John Irwin
Yeah I didn't think you meant tire storage for real but some are making suggestions based on some assumptions of what will and will not be under the overhang or whether or not doors will be left open. But somewhere a line has to be drawn. I can't protect against the grounds crew setting 10 gallo

RE: [EXTERNAL] Re: Exterior Play Area

2018-04-13 Thread Kyle.Montgomery
I was kidding. Probably should have added a smiley face or something. -Kyle M From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John Irwin Sent: Friday, April 13, 2018 12:56 PM To: sprinklerforum@lists.firesprinkler.org Cc: sprinklerforum@lists.firesprinkl

Re: Exterior Play Area

2018-04-13 Thread John Irwin
I was thinking about all the Porte Coches that I don't protect when looking at this job. I've done Porte Cochres larger than this and not needed protection. Personally I think idling cars present a higher risk of fire than a concrete basketball court. ⁣John Irwin  DynaFire Inc.  Tampa Fire Spri

Re: Exterior Play Area

2018-04-13 Thread bcasterline
In Kansas we call it a 'carport', or if it is only open on the front, a 'lean-to'. I will admit though, ~2000 s.f. of this is kind of scary. Good thing you excluded it John (hopefully you had it figured but it was just the dif between 20 and 25% profit. b. Quoting Bruce Verhei : In weste

Re: Exterior Play Area

2018-04-13 Thread Bruce Verhei
In western Washington we call it a rain shelter. Best. Bruce Verhei > On Apr 13, 2018, at 14:06, bcasterl...@fsc-inc.com wrote: > > It dosent say those things because it's outside the building Steve. > It's a shade structure, like you meant. Sprinklers would just make a big > mess. Open on th

RE: Exterior Play Area

2018-04-13 Thread Steve Leyton
No it ISN'T outside "the" building. It's attached and by definition it's a building and it doesn’t matter if it's open or not. If a fire starts under this structure it could spread to the building it's attached to easily - or are you 100% certain that a Boys and Girls Club is going to keep al

Re: Exterior Play Area

2018-04-13 Thread bcasterline
It dosent say those things because it's outside the building Steve. It's a shade structure, like you meant. Sprinklers would just make a big mess. Open on three sides and non-comb means no life safety issue and if that's where it starts it won't get inside before the FD gets there. These 12-

RE: Exterior Play Area

2018-04-13 Thread Steve Leyton
Y'all need to read the definition of "Building" in the Building Code: "Any structure used or intended for supporting or sheltering any use or occupancy." It doesn't mention walls or doors, it doesn't mention construction type or combustibility of materials. So the area in question IS a bu

RE: [EXTERNAL] Re: Exterior Play Area

2018-04-13 Thread John Irwin
I'm not sure assuming the worst is the way to go. Additionally, 2/3 of the covered area is concrete basketball court. ⁣John Irwin  DynaFire Inc.  Tampa Fire Sprinkler Division  727-282-9243  This email was sent from a mobile device. Please forgive brevity, typographical errors, and grammatical

Re: [EXTERNAL] Re: Exterior Play Area

2018-04-13 Thread Carrie Nickell
It has a concrete slab. On Fri, Apr 13, 2018 at 3:53 PM Kyle.Montgomery wrote: > Yeah, but that stuff they put on the ground is shredded tires. So... I > guess start looking at tire storage criteria. Probably go ESFR in that area. > > -Kyle M > > -Original Message- > From: Sprinklerforum

RE: [EXTERNAL] Re: Exterior Play Area

2018-04-13 Thread Kyle.Montgomery
Yeah, but that stuff they put on the ground is shredded tires. So... I guess start looking at tire storage criteria. Probably go ESFR in that area. -Kyle M -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of bcasterl...@fsc-inc.co

Re: Exterior Play Area

2018-04-13 Thread bcasterline
I vote no sprinklers required -- open and noncombustible- the rockinghorse on a spring is like a newspaper machine - there will always be just one of them- not one today and twelve tomorrow. Brad. Quoting Steve Leyton : 8.15.7.5. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists

RE: Exterior Play Area

2018-04-13 Thread Steve Leyton
8.15.7.5. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John Irwin Sent: Friday, April 13, 2018 11:10 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Exterior Play Area I can appreciate your opinion, but I need a code reference. 😉 John Irw

RE: Exterior Play Area

2018-04-13 Thread John Irwin
I can appreciate your opinion, but I need a code reference. 😉 John Irwin DynaFire Inc. – “*Same Day – Next Day*” *From:* Sprinklerforum *On Behalf Of *Steve Leyton *Sent:* Friday, April 13, 2018 1:47 PM *To:* sprinklerforum@lists.firesprinkler.org *Subject:* RE: Exterior Play Area Assum

RE: Exterior Play Area

2018-04-13 Thread Steve Leyton
Assuming there’s play equipment there (fire load) and knowing that there are kids occupying the space, I wouldn’t call this an “exterior projection”. It’s a shad structure with occupancy below and IMO requires sprinkler protection. SML From: Sprinklerforum [mailto:sprinklerforum-boun...@lists

Foam in spray rooms

2018-04-13 Thread Ben Young
I'm working on project that has a coating room that uses MEK and acetone. We were already protecting the exterior tanks with a foam deluge system, and now we've been asked to do a wet foam system in the coating room, the exhaust duct, and the dust collector. So this all falls under NFPA 33, I get

Exterior Play Area

2018-04-13 Thread John Irwin
Protecting a light hazard Boys and Girls Club. I excluded an exterior, but covered, attached and open play area. Non-combustible. It’s a couple thousand square feet. I excluded using NFPA 13 2013 8.15.7 Client is telling me that he her other fire sprinkler guys telling him he needs sprinklers in

RE: Expansion Joint

2018-04-13 Thread Russell & Carol Gregory
Victaulic have one which is a bunch of cut groove couplings with stubs of pipe between. As it uses couplings that would be Approved it should be Approvable if not already listed, Russell Gregory Christchurch New Zealand From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprink