RE: [EXTERNAL] 8 inch sprinkler pipe fall from factory ceiling

2022-02-25 Thread Scott Futrell via Sprinklerforum
Interesting discussion on this forum. Steve is utilizing the scientific method that needs to be used to avoid a Daubert challenge and ensure the proper conclusion, if there is one. Scott   Office: (763) 425-1001 x 2 Cell: (612) 759-5556 -Original Message- From: Sprinklerforum On Behalf

Re: [EXTERNAL] 8 inch sprinkler pipe fall from factory ceiling

2022-02-25 Thread Gary Howard, P. Eng. via Sprinklerforum
Thank you for this very detailed email. The website to check for wind that day is down. I will check. The possibility of the 8 inch riser (on a manifold with 4 other 8 inch risers that were downstream from the fire pump) is real. Unfortunately new pipe was installed before we could inspect. In

RE: [EXTERNAL] 8 inch sprinkler pipe fall from factory ceiling

2022-02-25 Thread Steve Leyton via Sprinklerforum
Fire sprinkler systems have historically been designed on what is called a "deferred submittal" basis, which means that the construction docs are already submitted or approved under a separate permit application. When sprinklers are put out to bid, the work has historically included establishi

Re: Sprinkler in elevator pit.

2022-02-25 Thread Kenneth Berman via Sprinklerforum
All elevators have pits. Most have shafts. Fire heat fuses the sprinkler when it banks down from the elevator car's floor. Otherwise the heat goes up the shaft. On Fri, Feb 25, 2022 at 12:32 PM Ed Kramer via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > Speculation only, but

Re: [EXTERNAL] 8 inch sprinkler pipe fall from factory ceiling

2022-02-25 Thread Gary Howard, P. Eng. via Sprinklerforum
I should note that it was windy when I was investigating 3 days after the event. I will check that for the date of loss. However, the clamps should redesigned to handle this, no? > On Feb 25, 2022, at 11:19 AM, John Hoffman via Sprinklerforum > wrote: > > How windy was it? Steel joisted bu

RE: Sprinkler in elevator pit.

2022-02-25 Thread Ed Kramer via Sprinklerforum
Speculation only, but maybe an "enclosed shaft" (in this context) is one in which debris originating from outside the shaft is unlikely to collect at the bottom of the shaft. Conversely, a shaft that is not enclosed can collect debris originating from outside the shaft. Or not. Ed Kramer

Re: Sprinkler in elevator pit.

2022-02-25 Thread AKS-Gmail-IMAP via Sprinklerforum
Wire cage elevators in industrial settings are often unenclosed. The original question, “What constitutes an “enclosed” shaft?”, I think is a question asking, “Is not a shaft enclosed by definition?”. That makes sense to me. In certain circumstances building codes require a shaft of specific wa

Re: Sprinkler in elevator pit.

2022-02-25 Thread Ron Greenman via Sprinklerforum
May be helpful. Maybe not. https://www.nfpa.org/News-and-Research/Publications-and-media/Blogs-Landing-Page/NFPA-Today/Blog-Posts/2019/11/20/101wednesdays-vertical-opening-protection-in-nfpa-101 On Fri, Feb 25, 2022 at 7:01 AM Ken Wagoner via Sprinklerforum < sprinklerforum@lists.firesprinkler.or

Re: [EXTERNAL] 8 inch sprinkler pipe fall from factory ceiling

2022-02-25 Thread John Hoffman via Sprinklerforum
How windy was it?  Steel joisted building roofs can move up and down a lot, several inches, in the wind.  Over time, this up and down could have an impact on the pipe support system.  You might check that and its potential affect on pipe hangers.  A structural engineer can probably look at the

Re: Sprinkler in elevator pit.

2022-02-25 Thread Ken Wagoner via Sprinklerforum
Todd, and Matt, Speculating here. Some time ago I stayed in a hotel which had a huge multi-story atrium, and along two of the four walls were elevators.  Both elevator "shafts" were open to the atrium for the length of travel, save for the pit at the bottom. That might be a shaft which is r