RE: MORE ACTIVITY WEIGHING IN

2021-02-17 Thread Anthony via Sprinklerforum
If you need a table showing the weight of the water filled pipe then we have an Excel sheet that is fillable to determine the weights. We often fill this out and send to the structural engineer. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-528

RE: Uprights in non combustible concealed space

2020-07-15 Thread Anthony via Sprinklerforum
e would have been putting sprinklers into concealed spaces for years and the NFPA 13 committee would have already harmonized the standard with the code. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Anthony via Sprinklerforum Sent: Wed

RE: Uprights in non combustible concealed space

2020-07-15 Thread Anthony via Sprinklerforum
All, in the IBC it says in section 903.3.1.1 NFPA 13 sprinkler systems. Where the provisions of this code require that a building or portion thereof be equipped throughout with an automatic sprinkler system in accordance with this section, sprinklers shall be installed throughout in accordance

RE: Minimum Lead-in Sizing

2020-03-18 Thread Anthony via Sprinklerforum
Perhaps they will accept what NFPA 13 states.. NFPA 13-2016 edition shows the size requirements 24.1.3* Size of Fire Mains. 24.1.3.1 Except as provided in 24.1.3.2 or 24.1.3.3, no pipe smaller than 6 in. (150 mm) in diameter shall be installed as a private service main. 24.1.3.2 For mains