All, in the IBC it says in section 903.3.1.1 NFPA 13 sprinkler systems. 

Where the provisions of this code require that a building or portion

thereof be equipped throughout with an automatic

sprinkler system in accordance with this section, sprinklers

shall be installed throughout in accordance with

NFPA 13 except as provided in Sections 903.3.1.1.1

and 903.3.1.1.2.

903.3.1.1.1 Exempt locations. Automatic sprinklers

shall not be required in the following rooms or

areas where such rooms or areas are protected with

an approved automatic fire detection system in

accordance with Section 907.2 that will respond to

visible or invisible particles of combustion. 

Sprinklers shall not be omitted from a room merely

because it is damp, of fire-resistance-rated construction

or contains electrical equipment.

4.Rooms or areas that are of noncombustible

construction with wholly noncombustible contents.

 

This non combustible area above the ceiling is not required to be
sprinklered per NFPA 13 but as mentioned in the IBC it's only if the area is
protected with approved automatic fire detection system.

You could check to see if this area has any smoke detectors and if not use
this section to show that the upright protection of a non-combustible area
is required per the IBC. 

 

 

Anthony Carrizosa 

Project Manager | Fire Protection 

7855 S 206th St Kent, WA 98032

Cell: 206-679-5283 | Office: 253-872-7222 

 



https://archerconstruction.com
<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%
2f&c=E,1,Wdb65AWzMgSBzW3HDw91SfcRQCtxDUQKoJf-UowQ-WnB_WMosgG-8W7eLePJ42PwWQv
LiQx16Pls052VqwHO7tKm-_u5AnWly0ewkNiMkxn-AjQb1JI,&typo=1> 

 

 

 

 

 

From: Cary Webber <cweb...@reliablesprinkler.com> 
Sent: Thursday, June 18, 2020 11:29 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Uprights in non combustible concealed space 

 

On the downside, if all areas above the ceilings are not protected, it may
give a false sense of security. On the upside, more sprinklers are better,
and even if not required they can act as detectors in the space. Bottom line
is that the AHJ has ultimate decision making authority.

 

 

 

Cary Webber CFPS Director, Technical Services

Reliable Automatic Sprinkler Co., Inc.

1470 Smith Grove Road, Liberty, SC  29657 

Tel: 864-843-5161 

 

 <http://www.reliablesprinkler.com/> 

 

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org
<mailto:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of John
Irwin via Sprinklerforum
Sent: Thursday, June 18, 2020 2:21 PM
To: sprinklerforum@lists.firesprinkler.org
<mailto:sprinklerforum@lists.firesprinkler.org> 
Cc: John Irwin <jir...@quickresponsefl.com
<mailto:jir...@quickresponsefl.com> >
Subject: Uprights in non combustible concealed space 

 

CAUTION: This email originated from outside of the organization. Do not
click links or open attachments unless you can confirm the sender and know
the content is safe. 

 

We installed temporary upright Protection in a partially occupied building
during a major renovation. We then came back and dropped pendent heads in
the new ceiling. We left the uprights above the new ceiling. Fire inspector
says we need to remove the uprights now. Is there a basis for removing
these? I realize they are not required but are they permitted to remain? 

 

John Irwin