Re: S & L Rule

2017-12-22 Thread Charles Bamford
30' x 20' =  600 sq ft600/ 130 = 4.6       round up  6 sprinkler heads Run Branch lines perpendicular to  what you are hanging from.5' off wall  10' between heads for100 sq ft per sprinkler head or15' x  6'8" (3'4" off wall) with smaller sq.ft. spacing you get less GPM per head in calcs.so if its

Re: RE: FDC sizing on wet automatic standpipes

2017-11-17 Thread Charles Bamford
4" pipe for 1000 gpm is very restrictive City of Redmond WA requires flow test,and we just did one. Here are our resultsRemote hose @  100 psi  260 gpm  level 510' lower on same standpipe    104 psi 290 gpm   level 4@ 2 other Restricted hose valves  110 psi 250 gpm15

Re: NFPA 13 8.17.5.2.2(1)

2017-08-31 Thread Charles Bamford
What type/brand of PRV are you using? Some manufactures have the listing below. "..Pressure ReducingValve is listed as a floor control valve, an indicating valve,and a check valve in automatic sprinkler systems as wellas a standpipe valve for CLASS I and CLASS III systems."These valves are 2

Re: Grow Facilities

2017-06-01 Thread Charles Bamford
rd plastic, Racks,   general storage? This is just a starting point questions. Arch/Engineers, AHJ's  are going to need to provide details. Charles Bamford SET On Wednesday, May 31, 2017 11:34 AM, "Travis Mack, SET" wrote: This is obviously outside of our scope and

Re: Never heard of this One

2017-03-06 Thread Charles Bamford
1.  Is this a remodel job with an old ceiling (installed per???) or a New ceiling/job? 2.  Where's the project? who is the AJH?  Southern California may have some additional requirements. Didn't the old brackets use to have a hole for 3/8" ATR? On Monday, March 6, 2017 10:10 AM, Mike Hai

Re: Artifical Turf

2017-02-01 Thread Charles Bamford
"Thoughts" ? Carpet (minimum)Engineer of recordOwner's Information CertificateType of storage ? rack length 15' of tube? bigger create a solid shelf?chapter 22? NFPA 30 Chuck Bamford SET   On Tuesday, January 31, 2017 4:48 PM, James Crawford wrote: We are looking at a client the store

Re: Selecting a Fire Pump/ Europeans vs. Americans

2017-01-30 Thread Charles Bamford
u're design is 1400 -1800 gpm--  Use a 1250 gpm pump. I would be concerned with a to big of pump sucking up "stuff"  and going below 20 psi residual. Charles Bamford SET On Monday, January 30, 2017 1:28 PM, Steve Leyton wrote: And if an area closer to the water supply - i.e.

Re: Ammunition Manufacturer

2017-01-20 Thread Charles Bamford
Paging Scott Mitchell.. On Friday, January 20, 2017 11:27 AM, "Hinson, Ryan" wrote: #yiv0109144994 #yiv0109144994 -- _filtered #yiv0109144994 {panose-1:2 4 5 3 5 4 6 3 2 4;} _filtered #yiv0109144994 {font-family:Calibri;panose-1:2 15 5 2 2 2 4 3 2 4;}#yiv0109144994 #yiv0109144

Re: DI Piping

2017-01-09 Thread Charles Bamford
"What I have is the contractor ran about 50’ and a couple turns of DI above ground between the BFP and where they switched to galvanized piping. It’s all outside in a non-freezing climate, also earthquake country. It’s mostly flanged connections and supported well with pipe stands. On the surfac

Re: 1.85 Graph

2016-12-07 Thread Charles Bamford
pingfire . com has an web based graph that you can change GPM  &  PSI I use a snipping tool & convert pdf Charles Bamford On Wednesday, December 7, 2016 6:30 AM, "wmens...@comcast.net" wrote: Does anyone have a blank 1.85 graph form you can send me?  Much appreci

Re: Roof Parapet Protection

2016-11-09 Thread Charles Bamford
Dry Uprights may work, if space is can be sprinklered with 48" or less. Chuck Bamford SET On Tuesday, November 8, 2016 8:33 AM, Steve Sorrell wrote: #yiv4679405160 #yiv4679405160 -- _filtered #yiv4679405160 {font-family:Calibri;panose-1:2 15 5 2 2 2 4 3 2 4;} _filtered #yiv4679405160

Re: Ordinary Hazard Attic Spacing

2016-10-17 Thread Charles Bamford
Acute Slopes, wood frame construction,Space the heads every 8' on Branch line and go up to 15' Up the slopeNFPA 13  2013 edtion Fig 8.6.4.1.4 Are you trying to call it Ordinary hazard to get out of this spacing requirements? Attic heads space every 6', and after testing standard spacing 10' 12' o

Re: Nitrogen Systems

2016-08-15 Thread Charles Bamford
H2O) and replace that area of Piping this is not an exact science. Charles Bamford SET http://ultimatefiresprinklerguide.com/Guide/SearchListing?searchTerm=nitrogen+generator&PageNo=1&PageSize=10§ionType=Keywords&categoryId=0&headingId=&Region=&rbPhraseType=2&StateProvi

Re: CPVC Systems

2016-08-04 Thread Charles Bamford
Here's some info on Spears CPVC,    I don't where or if its in code book ,   but has to do with its Listing.  Tees on Run and Coupling have an equivalent foot. Hydraulic DesignHydraulic calculations for the sizing of systems incorporating Spears®FlameGuard® CPVC Fire Sprinkler Products must be c

Re: Standpipe Test requirements

2016-07-15 Thread Charles Bamford
City of Redmond WA "A functional flow test shall be performed at your expense to prove the standpipe design as required for normal system acceptance procedures found in Chapter 9 of NFPA 14.    I. REQUEST FOR TEST  The contractor shall request this test in writing at least 3 weeks in advance...

Re: acid corosion

2016-07-14 Thread Charles Bamford
Have you reached out to any of the Nitrogen selling companies? maybe  Wet Pipe Nitrogen Inerting (WPNI) ?could solve the problem. On Wednesday, July 13, 2016 6:26 PM, AKS-Gmail-IMAP wrote: A suggestion: The Frat house has a CO2 system fed from the domestic water that is intended for

Re: Base of riser on placards

2016-07-12 Thread Charles Bamford
I've used BOR at transition from UG to aboveground pipe.(Easy to find on Hydraulics and thus find for Calc Plate) Calc Plate ,  use a Sharpie then go over with Engraver. @ 1 Main Drain test Static PSI was OK, then when opened main drainthe PSI dropped and we got a garden hose amount.The Cities ho

Re: EXTENDED COVERAGE SPRINKLERS

2016-06-28 Thread Charles Bamford
    11.2k Sounds like regular spacing 5.6k head maybe the choice. Charles Bamford, SET On Tuesday, June 28, 2016 3:05 AM, Lamar Vaughn wrote: Here is another way to approach this. You say you can protect the room with 7 standard coverage sprinklers and then calc a 923 sq.ft. area which wou

Re: FM Global Design Area

2016-06-27 Thread Charles Bamford
nfpa 13 2013 edition 23.4.4.3  4 sprinklers on 3 branchlines On Monday, June 27, 2016 11:25 AM, "Reed A. Roisum, SET" wrote: Having trouble finding where to determine how many sprinklers per line to include in a 12 sprinkler calc from FM Global.  I’ve looked through FMDS 2-0, 3-0, an

Re: K25 ESFR and plastic storage.

2016-06-23 Thread Charles Bamford
Ceiling height needs to be the Highest point within Storage area(example I have is 2/12 pitch roof) 25'6" will have a different psi starting PSIthan 24'6"just taking a quick glance,using NFPA 13 2013 edtiontable 17.2.3.1   may get a starting point. On Thursday, June 23, 2016 6:27 AM, Todd