Does the in-rack sprinkler system need to be combined with the ceiling
sprinkler system, for hydraulic calcs? Can anyone cite reference that requires
this?
V/R,
Timothy M. Easter, P.E.
NAVFAC Mid-Atlantic
Capital Improvements
Fire Protection Engineer
Comm: (757) 341 - 0130 / DSN 341 - 0130
If a head were to be knocked off it would essentially have the same effect. So
it makes no sense why a dry system is prohibited.
Feel free to contact me with any questions.
Regards,
Timothy Easter, PE
Fire Protection Engineer, Fire Protection
D +1-757-306-6712
I know you are using 2007 edition, but the 2013 edition's introduction states
"Further clarification
was also added stating that sprinklers are not required on balconies or balcony
closets."
Feel free to contact me with any questions.
Regards,
Timothy Easter, PE
Fire Protection Engineer, Fire
___
From: Sprinklerforum
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
on behalf of Easter, Timothy
<timothy.eas...@aecom.com<mailto:timothy.eas...@aecom.com>>
Sent: Wednesday, July 20, 2016 10:54:05 AM
To:
sprinklerfor
Can someone explain to me how variable speed electric controller and or diesel
pressure limiting driver work? We are worried about the fire pumps running the
city supply main dry. Any help would be appreciated, I just want a better
understanding, I have looked at presentations online through
What code and section states where fire protection systems are required? We
have a 2200sf new toilet building being installed near a wharf.
Feel free to contact me with any questions.
Regards,
Timothy Easter, PE
Fire Protection Engineer, Fire Protection
D +1-757-383-6217
I ALSO AGREE with Craig.
Craig, you are a great contributor. I sure have learned a lot from you, thank
you for your help!
Feel free to contact me with any questions.
Regards,
Timothy Easter, PE
Fire Protection Engineer, Fire Protection
D +1-757-383-6217
timothy.eas...@aecom.com
AECOM
11832
We are required by AFB to install a temperature monitoring system to monitor
wet-pipe sprinkler systems within hangars. Does anyone have any recommendations
i.e. specific manufacturer? How are these installed i.e. every other branch
line, or one in middle and at each corner?
Feel free to
Drive
Spartanburg, SC 29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension 74102
craig.pr...@ch2m.com
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Easter, Timothy
Sent: Wednesday, March 16, 2016 1:31 PM
Spartanburg, SC 29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension 74102
craig.pr...@ch2m.com
Original message
From: "Easter, Timothy" <timothy.eas...@aecom.com>
Date: 3/16/2016 8:08 AM (GMT-08:00)
To: sprinklerforum@lists.firesprinkler.org
Subject:
How to estimate the GPM for radiator blowoff (diesel fire pump, YES it has a
radiator :)) so we can confirm the floor drain pipe will handle it?
Feel free to contact me with any questions.
Regards,
Timothy Easter, P.E.
Fire Protection Engineer
Direct: (757) 383-6217
How to estimate the GPM for radiator blowoff (diesel fire pump, YES it has a
radiator :)) so we can confirm the floor drain pipe will handle it?
Feel free to contact me with any questions.
Regards,
Timothy Easter, P.E.
Fire Protection Engineer
Direct: (757) 383-6217
We have an 8" pressure relief valve and floor drain piped directly to storm,
but apparently have not accounted for the radiator discharge line (either
1-1/2" or 2"). It currently blows out into the yard during their weekly tests.
The Client says it can be piped to storm as well; but that they
Can anyone provide me with re-commissioning guidelines/recommendations for
installation of a diesel fire pump? Basically, we are moving an entire fire
pump enclosure to a new location. I currently have the storage recommendations
but do not have the re-commission recommendations. This is a
Is there an actual requirement during acceptance testing of foam systems to
conduct a 72 or 90 hour battery test on the Foam panel and the foam
controllers, if so where is the information located? I have a contractor
telling me its required.
Feel free to contact me with any questions.
ting.com/> *** On 10/14/2015 1:40
PM, Easter, Timothy wrote:
> The facility is a non-combustible business occupancy. Basically, two office
> areas were converted into a small work out area by removing a wall and
> raising a section of the ceiling. The section that is higher has no sprinkler
&
The facility is a non-combustible business occupancy. Basically, two office
areas were converted into a small work out area by removing a wall and raising
a section of the ceiling. The section that is higher has no sprinkler heads in
it leaving a void above all other lower sprinkler heads. The
I am designing a sand blasting room as ordinary hazard group 2. Is this
acceptable? Should it be a higher hazard? Is there another NFPA code pertaining
to a sand blasting room?
Feel free to contact me with any questions.
Regards,
Timothy Easter
E.I.T.
Graduate Fire Protection Engineer
URS
What is the difference between surge suppressor and expansion tanks used for
pumps and risers?
Feel free to contact me with any questions.
Regards,
Timothy Easter
11832 Rock Landing Drive Suite 306
Newport News, VA 23606
Direct: (757) 383-6217
Does anyone know/have a copy of gasket datasheet, for use between flanges
connection in the foam concentrate piping? If so, please send me a copy.
Regards,
Timothy Easter
11832 Rock Landing Drive Suite 306
Newport News, VA 23606
Direct: (757) 383-6217
UFGS states segmented welded fittings shall not be used. What is a segmented
welded fitting?
Thanks,
Timothy Easter
E.I.T.
Graduate Fire Protection Engineer
This e-mail and any attachments contain URS Corporation confidential
information that may be proprietary or privileged. If you receive
For example in data centers, I thought it would be a good idea to have floor
drains (under raised floors) installed for water removal upon sprinkler
discharge. However, I was told no requirement exist. Does a requirement exist
that I can't find. Thanks.
Regards,
Timothy Easter
E.I.T.
Graduate
Designer is required to do a forward flow test for BFP. However, the riser is
existing to remain, and does not have a test header. How can a forward backflow
test be done?
Regards,
Timothy Easter
E.I.T.
Graduate Fire Protection Engineer
This e-mail and any attachments contain URS
I know smoke detectors are required within 5' of FACP/MNS panels, what about
fire pump controller panels?
Regards,
Timothy Easter
E.I.T.
Graduate Fire Protection Engineer
URS Corporation
This e-mail and any attachments contain URS Corporation confidential
information that may be proprietary
Is a UPS room considered light or ordinary hazard?
I classify electrical and mechanical rooms as ordinary hazard.
So my logic is UPS rooms should be too.
Regards,
Timothy Easter
E.I.T.
Graduate Fire Protection Engineer
URS Corporation
This e-mail and any attachments contain URS Corporation
Does a carport require sprinkler protection or detection?
Regards,
Timothy Easter
E.I.T.
Graduate Fire Protection Engineer
URS Corporation
11832 Rock Landing Drive Suite 306
Newport News, VA 23606
Direct: (757) 383-6217
timothy.eas...@urs.commailto:timothy.eas...@urs.com
This e-mail and any
I am use to providing one 2 ½ connection for every 250 gpm of system demand.
I do not know where this requirement came from nor do I know of any
requirement. Does anyone know of such a requirement?
Regards,
Timothy Easter
E.I.T.
Graduate Fire Protection Engineer
URS Corporation
11832 Rock
I am reviewing a dormitory. The designer used the room design method (laundry,
telephone room, and corridor), special consideration method - residential heads
(bedrooms), and the density/area method (day room, computer lab). He is using
NFPA 13, and not NFPA 13R.
Basically he needs to increase
Are sprinklers required in an unenclosed corridor directly outside dwelling
units? Building is supposed to be fully sprinklered.
Regards,
Timothy Easter
E.I.T.
Graduate Fire Protection Engineer
URS Corporation
11832 Rock Landing Drive Suite 306
Newport News, VA 23606
Direct: (757) 383-6217
Fax:
I am told to provide a sleeve for the underground piping that penetrates the
floor to riser.
I can't find any nfpa code that requires this.
Help.
Regards,
Timothy Easter
E.I.T.
Graduate Fire Protection Engineer
URS Corporation
11832 Rock Landing Drive Suite 306
Newport News, VA 23606
Direct:
What is the difference between cmsa and cmda sprinkler heads?
Regards,
Timothy Easter
Fire Protection Designer
URS Corporation
11832 Rock Landing Drive Suite 306
Newport News, VA 23606
Direct: (757) 383-6217
Fax: (757) 873-0634
timothy.eas...@urs.commailto:timothy.eas...@urs.com
This e-mail
What is the difference between alarm check valve versus riser check valve? Is
it just that an alarm check valve has a retard chamber?
Regards,
Timothy Easter
Fire Protection Designer
URS Corporation
11832 Rock Landing Drive Suite 306
Newport News, VA 23606
Direct: (757) 383-6217
Fax: (757)
Doing a government project, where in UFC, IBC, NFPA 72/101 can I find exception
that man-trap do not need smoke detectors? This is an un-sprinklered
non-essential building. Thanks.
Regards,
Timothy Easter
Fire Protection Designer
URS Corporation
11832 Rock Landing Drive Suite 306
Newport News,
We use NFPA 101 to determine occupant load factor. The project I have is a
small storage facility, the designer used 100 sf/person for occupant load
factor. But where in NFPA 101 does it state that occupant load can be omitted
from bathrooms or that 100 sf/person is right? Thanks. We cannot use
According to UFC 3-600-01 FRT plywood is prohibited except where allowed in
IBC. I can't find anything in IBC that states where its allowed. I have a
mechanical room with electrical equipment being attached to three interior
walls with FRT plywood. The exterior wall is concrete block 1 hour