From: Bob Knight via Sprinklerforum
To:
Cc: Bob Knight
Date: 06/16/2020 07:34 PM
Subject: RE: [EXTERNAL] RE: Floor area less than re
Cc: Bob Knight mailto:b...@firebyknight.com>>
Subject: RE: [EXTERNAL] RE: Floor area less than required
The spec is demanding 8.0K for the LH areas.
Thank you,
Bob Knight, CET III
Fire by Knight, LLC
208-318-3057
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Be
> Behalf Of Bob Knight via Sprinklerforum
> Sent: Tuesday, June 16, 2020 6:50 PM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Bob Knight
> Subject: RE: [EXTERNAL] RE: Floor area less than required
>
>
> The spec is demanding 8.0K for the LH areas.
klerforum *On
> Behalf Of *Bob Knight via Sprinklerforum
> *Sent:* Tuesday, June 16, 2020 6:50 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Cc:* Bob Knight
> *Subject:* RE: [EXTERNAL] RE: Floor area less than required
>
>
>
> The spec is demanding 8.0K for the
Bob Knight via Sprinklerforum
Sent: Tuesday, June 16, 2020 6:50 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Bob Knight
Subject: RE: [EXTERNAL] RE: Floor area less than required
The spec is demanding 8.0K for the LH areas.
Thank you,
Bob Knight, CET III
Fire by Knight, LLC
208-318-3057
Don’t you just love them engineers!!!
[cid:image001.jpg@01D64479.C843B3A0]
From: Sprinklerforum On Behalf
Of Bob Knight via Sprinklerforum
Sent: Tuesday, June 16, 2020 6:50 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Bob Knight
Subject: RE: [EXTERNAL] RE: Floor area less than required
rtes, 16 de junio de 2020 19:03
Para: sprinklerforum@lists.firesprinkler.org
CC: Bob Knight
Asunto: RE: [EXTERNAL] RE: Floor area less than required
I just didn’t use the entire number. It seemed obscene for what’s being
protected.
But, technocrats are on the job, so the actual number came in a
...@lists.firesprinkler.org] On
Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Sent: Tuesday, June 16, 2020 6:00 PM
To: b...@firebyknight.com; sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G
Subject: RE: [EXTERNAL] RE: Floor area less than required
Sqrt
ay, June 16, 2020 4:50 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Bob Knight
Subject: RE: [EXTERNAL] RE: Floor area less than required
The spec is demanding 8.0K for the LH areas.
Thank you,
Bob Knight, CET III
Fire by Knight, LLC
208-318-3057
From: Sprinklerforum [mailto:sp
;
>
>
> From:Sprinklerforum
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Travis
> Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
> Sent: Tuesday, June 16, 2020 5:48 PM
> To: b...@firebyknight.com; sprinklerforum@lists.firesprinkl
, 2020 5:48 PM
To: b...@firebyknight.com; sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G
Subject: RE: [EXTERNAL] RE: Floor area less than required
4.2k or even 2.8k can be your friend – if applicable.
<http://www.mfpdesign.com/> MFP_logo_F
Travis Mack
http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/n1gewi5ud95byeftyuoy12/external?email=true&a=6&p=2591775&t=517003>
Android devices**
From: Sprinklerforum On Behalf
Of Bob Knight via Sprinklerforum
Sent: Tuesday, June 16, 2020 4:34 PM
To: sprinklerforum@lists.fir
, 2020 5:33 PM
To: b...@firebyknight.com; sprinklerforum@lists.firesprinkler.org
Cc: Kyle.Montgomery
Subject: RE: [EXTERNAL] RE: Floor area less than required
That sounds correct.
It seems strange that your calculation is over-discharging by more than 100%
though. Minimum discharge is 90 GPM and
Sprinklerforum
Sent: Tuesday, June 16, 2020 3:27 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Bob Knight
Subject: [EXTERNAL] RE: Floor area less than required
So, in this case I’m discharging over 200 gpm due to the number of sprinklers
in the area. Based on this I shouldn’t need to add any