Subject: RE: 13R Installation of Sprinkler Systems in Low-Rise Residential
Occupancies
Good call Sal; as I said in my response, it's up to the Building Official to
clarify whether that separation has to be two or three
tston...@comcast.net
>
> -Original Message-
> From: Steve Leyton
> Sent: Tuesday, November 9, 2021 3:51 PM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: tston...@comcast.net
> Subject: RE: 13R Installation of Sprinkler Systems in Low-Rise
> Residential Occ
sts.firesprinkler.org
Cc: tston...@comcast.net
Subject: 13R Installation of Sprinkler Systems in Low-Rise Residential
Occupancies
Am I reading the Scope of 13R correctly?
I am designing a Sprinkler system for a building which is five stories in
height. Each floor is about 5,500 SF. The Ground f
t; -Original Message-
> From: Steve Leyton
> Sent: Tuesday, November 9, 2021 3:51 PM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: tston...@comcast.net
> Subject: RE: 13R Installation of Sprinkler Systems in Low-Rise Residential
> Occupancies
>
> Assuming th
Salina, KSĀ 67401
-Original Message-
From: Sprinklerforum On
Behalf Of tstone52--- via Sprinklerforum
Sent: Tuesday, November 9, 2021 2:42 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: tston...@comcast.net
Subject: 13R Installation of Sprinkler Systems in Low-Rise Residential
Occupan
...@comcast.net
Subject: RE: 13R Installation of Sprinkler Systems in Low-Rise Residential
Occupancies
Assuming the building code that's applicable to this project classifies this
as two separate buildings (a four-story Type 3 on a single-story Type 1
podium), NFPA 13R can be used as a basis of design in
Is there a Code information sheet from the architect? Check to see what
allowances have been taken.
Is the separation enough for this to be treated as two buildings or is it a
single building?
My gut answer says no to 13R but the differences in construction could make a
dif
esday, November 09, 2021 12:42 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: tston...@comcast.net
Subject: 13R Installation of Sprinkler Systems in Low-Rise Residential
Occupancies
Am I reading the Scope of 13R correctly?
I am designing a Sprinkler system for a building which is five stori
Am I reading the Scope of 13R correctly?
I am designing a Sprinkler system for a building which is five stories in
height. Each floor is about 5,500 SF. The Ground floor is a parking garage
of concrete & steel (Type 1a construction) with 4 stories of Residential
above which constructed of wood