Re: [EXTERNAL] Re: Autopeak

2019-04-11 Thread J H
e 0.5 psi, it’s probably > worth the time to perform the manual peaking. > > > > -Kyle M > > > > *From:* Sprinklerforum [mailto: > sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *J H > *Sent:* Wednesday, April 10, 2019 5:00 PM > *To:* sprinklerforum

RE: [EXTERNAL] Re: Autopeak

2019-04-11 Thread Kyle . Montgomery
the time to perform the manual peaking. -Kyle M From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of J H Sent: Wednesday, April 10, 2019 5:00 PM To: sprinklerforum@lists.firesprinkler.org Subject: [EXTERNAL] Re: Autopeak On the non-typical grids it's pretty

Re: Autopeak

2019-04-10 Thread J H
On the non-typical grids it's pretty easy to identify your most demanding area. I just calc it w/o auto peak activated and submit. For grid systems with more typical spacing I'll peak it but have rarely ever had the hydraulic program correct my first attempt.

Re: Autopeak

2019-04-10 Thread Travis Mack
Not to be sarcastic, but I’ve never found a clause in NFPA 13 that says you don’t have to calculate something because it is time consuming. I just take it and shift the remote area right and left to prove. With most software packages today, doing extra calcs for peaking is usually pretty

Autopeak

2019-04-10 Thread Joe Burtell
Is there anything in NFPA 13 that discusses auto peaking if you have a grid in let's say an office space that is all cut up? Seems almost impossible to do it without drawings remote areas manually and calculating several groups of rooms. Best regards, *Joe Burtell, SET, CFPS* [image: Burtell