Re: In-Rack Sprinklers Required for CMSA

2018-03-29 Thread Lange, Drew A CIV USARMY CEHNC (US)
: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Parsley Consulting Sent: Thursday, March 29, 2018 10:34 AM To: sprinklerforum@lists.firesprinkler.org Subject: [Non-DoD Source] Re: In-Rack Sprinklers Required for CMSA Drew, Here's my thought for what

Re: In-Rack Sprinklers Required for CMSA

2018-03-29 Thread Parsley Consulting
Drew, Here's my thought for what it's worth.  It was not addressed by the discharge committee and wasn't noticed by the Correlating Committee.  If you look one chapter earlier in 16.2.2.7.1 the concern you have _*was*_ and is addressed by the following text [all emphasis is mine]: 16.2.2.

In-Rack Sprinklers Required for CMSA

2018-03-29 Thread Lange, Drew A CIV USARMY CEHNC (US)
Hello all! Long time listener, first time caller. NFPA 13 (2016 version) 17.2.2.6.1 reads "In-rack sprinklers shall be installed at the first tier level at or above one-half of the storage height." Could you confirm 17.2.2.6.1 doesn't REQUIRE in-rack sprinklers, and only identifies HOW to ins