Subject: [Non-DoD Source] Re: In-Rack Sprinklers Required for CMSA
Drew,
Here's my thought for what
Drew,
Here's my thought for what it's worth. It was not addressed by the
discharge committee and wasn't noticed by the Correlating Committee. If
you look one chapter earlier in 16.2.2.7.1 the concern you have _*was*_
and is addressed by the following text [all emphasis is mine]:
16.2.2.
Hello all! Long time listener, first time caller.
NFPA 13 (2016 version) 17.2.2.6.1 reads "In-rack sprinklers shall be installed
at the first tier level at or above one-half of the storage height." Could you
confirm 17.2.2.6.1 doesn't REQUIRE in-rack sprinklers, and only identifies HOW
to ins