[Sprinklerforum] Re: Old pipe Schedule system

2024-08-01 Thread cw bamford
10 x 10 = 100 sqft/sprinkler x .6 = 60 gpm/sprinkler Q=K sqrt(P) 60= 5.6 sqrt(P) P =115 psi Ouch please check my math 2000 sq ft / 100 = calc 20 or more heads sqrt 2000 x 1.2 = 53.7' calc 6 heads on line .6/2000 = + 1200 gpm probably closer to 1400 gpm 8" main? 150 psi at Riser o

[Sprinklerforum] Re: Old pipe Schedule system

2024-07-31 Thread Fpdcdesign
> > > https://calendly.com/t_mack_mepcad > > > > From: Bobby Welch > Sent: Wednesday, July 31, 2024 4:11:17 PM > To: sprinklerforum@lists.firesprinkler.org > > Subject: [Sprinklerforum] Old pipe Schedule system > > > >

[Sprinklerforum] Re: Old pipe Schedule system

2024-07-31 Thread Brett Peters
NFPA 13, 2016 12.6.1 For storage applications with densities of 0.2 gpm/ft2 (8.1 mm/min) or less, standard response sprinklers with a K-factor of K-5.6 (80) or larger shall be permitted. 12.6.2 For general storage applications, rack storage, rubber tire storage, roll paper storage, and baled cott

[Sprinklerforum] Re: Old pipe Schedule system

2024-07-31 Thread Travis Mack
NK RVT | AlarmCAD Book appointment time in my calendar https://calendly.com/t_mack_mepcad From: Bobby Welch Sent: Wednesday, July 31, 2024 4:11:17 PM To: sprinklerforum@lists.firesprinkler.org Subject: [Sprinklerforum] Old pipe Schedule system I am workin

[Sprinklerforum] Old pipe Schedule system

2024-07-31 Thread Bobby Welch
I am working on a project that looks to be an old pipe scheduled system. the branch line schedule is 1", 1", 1.25", 1.5", 1.5", 2" and the heads appear to be ½" 5.6K sprinklers. The spacing is 10' x 10' on the heads. There is a placard on the riser that states the area was calculated at a 0.60 o

Re: Old pipe schedule

2016-03-20 Thread Todd Williams
um [mailto:sprinklerforum-boun...@lists.firesprinkler.org] > On Behalf Of Matthew J Willis > Sent: Wednesday, March 16, 2016 7:46 AM > To: sprinklerforum@lists.firesprinkler.org > Subject: RE: Old pipe schedule > > Ah.., but the crux is, Are you working there under 25 or 13? > &

RE: Old pipe schedule

2016-03-19 Thread Brad Casterline
OUCH, Brad -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Matthew J Willis Sent: Wednesday, March 16, 2016 7:46 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Old pipe schedule Ah.., but the crux is, Are you wor

RE: Old pipe schedule

2016-03-19 Thread Matthew J Willis
- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Art Tiroly Sent: Wednesday, March 16, 2016 6:25 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Old pipe schedule What is the sprinkler spacing? Staggered spacing was quite common before 1940. Newer

RE: Old pipe schedule

2016-03-19 Thread Art Tiroly
Protection -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd Williams Sent: Wednesday, March 16, 2016 7:22 AM To: sprinklerforum@lists.firesprinkler.org Subject: Old pipe schedule I am working on a project in a mill that was

Re: Old pipe schedule

2016-03-19 Thread Brad Casterline
Todd, google 'history of fire protection' and look for rules ~1899 I think- it shows pipe schedule-- Or I could send the pdf when I get to the office 1.5 hours. Brad On Mar 16, 2016 6:22 AM, "Todd Williams" wrote: > I am working on a project in a mill that was constructed in 1884. On the > t

RE: Old pipe schedule

2016-03-19 Thread Richard Carr
...@coxfire.com 904-781-8227 -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd Williams Sent: Wednesday, March 16, 2016 7:22 AM To: sprinklerforum@lists.firesprinkler.org Subject: Old pipe schedule I am working on a project in a

RE: Old pipe schedule

2016-03-19 Thread Matthew J Willis
: Old pipe schedule I am working on a project in a mill that was constructed in 1884. On the top floor, the branch piping is 3/4 - 1 - 1. Was there an older version of pipe schedule that allowed smaller pipe or is this just undersized? Hopefully some of you history buffs (or at least those with a bun

Re: Old pipe schedule

2016-03-19 Thread Brad Casterline
> > > > > > -Original Message- > > From: Sprinklerforum [mailto: > sprinklerforum-boun...@lists.firesprinkler.org] > > On Behalf Of Matthew J Willis > > Sent: Wednesday, March 16, 2016 7:46 AM > > To: sprinklerforum@lists.firesprinkler.org > > Subject:

Re: Old pipe schedule

2016-03-19 Thread Lamar Vaughn
ler.org] On Behalf Of Art Tiroly > Sent: Wednesday, March 16, 2016 6:25 AM > To: sprinklerforum@lists.firesprinkler.org > Subject: RE: Old pipe schedule > > What is the sprinkler spacing? > Staggered spacing was quite common before 1940. > Newer heads installed? > High pressure water

Re: Old pipe schedule

2016-03-19 Thread Bruce Verhei
gt; -Original Message- > From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] > On Behalf Of Matthew J Willis > Sent: Wednesday, March 16, 2016 7:46 AM > To: sprinklerforum@lists.firesprinkler.org > Subject: RE: Old pipe schedule > > Ah.., but t

Re: Old pipe schedule "quick-response"

2016-03-19 Thread ACCENTFIRE
rforum-boun...@lists.firesprinkler.org] > On Behalf Of Matthew J Willis > Sent: Wednesday, March 16, 2016 7:46 AM > To: sprinklerforum@lists.firesprinkler.org > Subject: RE: Old pipe schedule > > Ah.., but the crux is, Are you working there under 25 or 13? > > R/ > Matt

Old pipe schedule

2016-03-18 Thread Todd Williams
I am working on a project in a mill that was constructed in 1884. On the top floor, the branch piping is 3/4 - 1 - 1. Was there an older version of pipe schedule that allowed smaller pipe or is this just undersized? Hopefully some of you history buffs (or at least those with a bunch of old stuf