Well in my current situation we are doing a pump replacements, so I have 24"
manifold in a trench with 12" leads popping up to 4 fire pumps then dropping
back down to 18" manifold in another trench. With the existing pump pads it
puts the 12" up about 3'6". I was hope to avoid having to put in brac
ssage-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of J. Scott Mitchell, PE
Sent: Wednesday, January 07, 2015 8:52 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Bracing for Pipe on Pipe Stands
Doesn't NFPA 13 allow engineer certifi
Doesn't NFPA 13 allow engineer certified bracing components to be used in lieu
of listed components?
Sent from my Verizon Wireless 4G LTE smartphone
Original message From: Jerry Van Kolken
Date:01/07/2015 4:43 PM (GMT-06:00)
To: sprinklerforum@lists.firesprinkler.org Subjec
No matter how well reinforced and clamped I'd consider a pipe stand
equivalent to a hanger (upside down). If the stands are holding up long
runs of pipe I'd brace them as if they were hanging from the ceiling. If
merely a couple of stands to support a back flow I'd look at the device and
associated
We've had to brace piping that was clamped to stands that were bolted to
the floor into 4 epoxied inserts. Whether we agree or disagree with
the enforcer, it's purely subjective as there's no exception in the
standard.
Adding a couple angled two-ways here and there isn't such a big deal
thoug