RE: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage

2021-07-02 Thread Matt Grise via Sprinklerforum
I missed that. > > Pete > > -Original Message- > From: Sprinklerforum > On Behalf Of Dane Long via Sprinklerforum > Sent: Thursday, July 1, 2021 12:51 PM > To: sprinklerforum@lists.firesprinkler.org > Cc: Dane Long ; Larrimer, Peter A (HEFP\19HEF) > > Subject: [EXTERN

Re: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage

2021-07-01 Thread Bob Caputo via Sprinklerforum
f Dane Long via Sprinklerforum >> Sent: Thursday, July 1, 2021 12:51 PM >> To: sprinklerforum@lists.firesprinkler.org >> Cc: Dane Long ; Larrimer, Peter A (HEFP\19HEF) >> >> Subject: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage >> >> Peter, >&

RE: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage

2021-07-01 Thread BRUCE VERHEI via Sprinklerforum
> -Original Message- > From: Sprinklerforum On > Behalf Of Dane Long via Sprinklerforum > Sent: Thursday, July 1, 2021 12:51 PM > To: sprinklerforum@lists.firesprinkler.org > Cc: Dane Long ; Larrimer, Peter A (HEFP\19HEF) > > Subject: [EXTERNAL] RE: Closets an

RE: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage

2021-07-01 Thread Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum
: Closets and Clearance from Deflector to Storage Peter, One thing to emphasize is that it says 400ft3 not ft2. So, the thought is if you have mechanical equipment like a furnace, you're not really going to have much room to store anything in this closet. An example would be a closet

RE: Closets and Clearance from Deflector to Storage

2021-07-01 Thread Dane Long via Sprinklerforum
Peter, One thing to emphasize is that it says 400ft3 not ft2. So, the thought is if you have mechanical equipment like a furnace, you're not really going to have much room to store anything in this closet. An example would be a closet with an 8ft. ceiling can only be 7ftx7ft. This is 49sqft or

RE: Closets and Clearance from Deflector to Storage

2021-07-01 Thread Bob Caputo via Sprinklerforum
Pete, You are correct. Where the closet is less than 400 ft3, no clearance is required below the deflector Bob Caputo -Original Message- From: Sprinklerforum On Behalf Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum Sent: Thursday, July 1, 2021 10:36 AM To:

RE: Closets and Clearance from Deflector to Storage

2021-07-01 Thread Mike Morey via Sprinklerforum
My understanding had always been this was mainly related to shelves and the like as an obstruction since the head is going to basically inundate the closet. I believe it was Mr. Huggins that once reminded us that water isn't like light and you don't have to see the head to get wet, as was a