Ugly". (I personally love the BB sprinklers for
> attic's.)
>
> -Original Message-
> From: sprinklerforum-boun...@firesprinkler.org
> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris
> Sent: Monday, April 25, 2011 9:10 AM
> To: sp
sage-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris
Sent: Monday, April 25, 2011 9:10 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: EC Sidewall Heads
And there you have it. I even had it highlighted in my book and still
, 2011 11:00 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: EC Sidewall Heads
NFPA #13 (2007)
8.7.3.1.4 Sidewall spray sprinklers shall not be installed back-to-back
without being separated by a continuous lintel or soffit.
On Mon, Apr 25, 2011 at 7:35 AM, Eric Tysinger wrote:
> Well NFPA
sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris
> Sent: Monday, April 25, 2011 10:25 AM
> To: sprinklerforum@firesprinkler.org
> Subject: RE: EC Sidewall Heads
>
> I talked with one of the engineers at Victaulic and he said installing them
> back to back would not
rforum-boun...@firesprinkler.org] On Behalf Of Eric
> Tysinger
> Sent: Monday, April 25, 2011 10:35 AM
> To: sprinklerforum@firesprinkler.org
> Subject: RE: EC Sidewall Heads
>
> Well NFPA 13 doesn't address sidewalls installed back to back (that I could
> quickly find). I
and if he is willing to put that advice into writing then I would believe
him.
Garth
- Original Message -
From: "Brian Harris"
To:
Sent: Monday, April 25, 2011 10:24 AM
Subject: RE: EC Sidewall Heads
I talked with one of the engineers at Victaulic and he said insta
: sprinklerforum@firesprinkler.org
Subject: RE: EC Sidewall Heads
Well NFPA 13 doesn't address sidewalls installed back to back (that I could
quickly find). Is there a beam that runs down the peak that you would be
hanging the line under? If so you would have to come out each side then up
into the p
forum-boun...@firesprinkler.org] On Behalf Of Brian Harris
Sent: Monday, April 25, 2011 10:25 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: EC Sidewall Heads
I talked with one of the engineers at Victaulic and he said installing them
back to back would not be a problem, I asked if the
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Eric Tysinger
Sent: Monday, April 25, 2011 10:20 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: EC Sidewall Heads
As you know smooth and flat doesn't mean it has to be horizontal. However
the exposed timber makes it not smoot
As you know smooth and flat doesn't mean it has to be horizontal. However the
exposed timber makes it not smooth and flat anymore. I think and I may be
wrong, but if you were to individually protect each pocket with a sidewall
sprinkler it may be acceptable, but where you are going to run into a
AS a reminder, there is an AFSA Reference Guide for Automatic
Sprinklers that identifies all such information.
Roland
On Mar 10, 2010, at 7:19 AM, Brian Harris wrote:
>
> Is there a sidewall head that throws 28ft. ? Any help would be greatly
> appreciated.
>
> Thanks!
> Brian
>
>
>
> _
John Denhardt
Sent: Wednesday, March 10, 2010 11:23 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: EC Sidewall Heads
No such sprinkler is currently available and I do not think every will be
available. Does it have to be quick response?
John August Denhardt, P.E.
Strickland Fire Prote
Subject: RE: EC Sidewall Heads
I actually need it to throw 28ft. (perpendicular to the pipe)
Brian Harris
FDFP INC.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Travis
Mack,
SET
Sent: Wednesday, March 10, 2010
: sprinklerforum@firesprinkler.org
Subject: Re: EC Sidewall Heads
Reliable makes a head that is 28' x 10' or something like that. Check the
DH56 and DH80 heads.
On 3/10/2010 8:28 AM, Brian Harris wrote:
> I'm talking "room width", I have a room that is 27' wide and would
&
-Original Message-
>From: sprinklerforum-boun...@firesprinkler.org
>[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
>Sent: Wednesday, March 10, 2010 10:26 AM
>To: sprinklerforum@firesprinkler.org
>Subject: Re: EC Sidewall Heads
>
>Sideways
>
&g
inkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris
Sent: Wednesday, March 10, 2010 8:28 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: EC Sidewall Heads
I'm talking "room width", I have a room that is 27' wide and would like to
cover it with one r
heads.
>
>
> Brian Harris
> FDFP INC.
>
> -Original Message-
> From: sprinklerforum-boun...@firesprinkler.org
> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
> Sent: Wednesday, March 10, 2010 10:26 AM
> To: sprinklerforum@firesprinkler.org
f Todd Williams
Sent: Wednesday, March 10, 2010 10:26 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: EC Sidewall Heads
Sideways
At 10:19 AM 3/10/2010, you wrote:
>
> Is there a sidewall head that throws 28ft. ? Any help would be
>greatly a
Sideways
At 10:19 AM 3/10/2010, you wrote:
>
> Is there a sidewall head that throws 28ft. ? Any help would be greatly
>appreciated.
>
>Thanks!
>Brian
>
>
>
>___
>Sprinklerforum mailing list
>Sprinklerforum@firesprinkler.org
>http://fireball.firesprinkl
19 matches