is applied to.
-Kyle M
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
Travis Mack
Sent: Friday, April 13, 2018 3:55 PM
To:
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [EXTERNAL] Re: Exterior
less
than 2,000 sq. ft.? I can admit that this is a larger area than I would
normally see this applied to.
-Kyle M
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Travis Mack
Sent: Friday, April 13, 2018 3:55 PM
To:
sprinklerforum@lists.firesprinkler.org
if there is no combustible
>storage.
>>>>
>>>>
>>>> Show me where the building code says otherwise… and then show me
>how this area is different than other exterior projections where
>sprinkler may be omitted.
>>>>
>>>>
>>>> “A.8.15
terior projections include, but are not limited to, exterior
>>> roofs, canopies, porte-cocheres, balconies, decks, or similar projections.”
>>>
>>>
>>> Is there a definition of “exterior projection” somewhere that limits it to
>>> less than 2,000
projection” somewhere that limits
>it to less than 2,000 sq. ft.? I can admit that this is a larger area
>than I would normally see this applied to.
>>
>> -Kyle M
>>
>> From: Sprinklerforum
>[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
>Travis Mack
would
> normally see this applied to.
>
> -Kyle M
>
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of Travis Mack
> Sent: Friday, April 13, 2018 3:55 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: [EXTERNAL] Re: Exterior Play Ar
@lists.firesprinkler.org
Subject: [EXTERNAL] Re: Exterior Play Area
We need a LIKE button for emails. So many times people get lost debating NFPA
13 criteria when the answer is quite clear in the building code.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook:
https://www.facebook.com
in the IBC.This is a
building.
SML
-Original Message-
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf
Of bcasterl...@fsc-inc.com
Sent: Friday, April 13, 2018 2:07 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Exterior Play Area
It do
Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of bcasterl...@fsc-inc.com
> Sent: Friday, April 13, 2018 2:07 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: Exterior Play Area
>
> It dosent say those things because it's ou
boun...@lists.firesprinkler.org] On Behalf Of
John Irwin
Sent: Friday, April 13, 2018 12:56 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] Re: Exterior Play Area
I'm not sure assuming the worst is the way to go. Additiona
g
Cc: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] Re: Exterior Play Area
I'm not sure assuming the worst is the way to go. Additionally, 2/3 of
the covered area is concrete basketball court.
John Irwin
DynaFire Inc.
Tampa Fire Sprinkler Division
727-282-9243
This email was sent from a mobi
Sent: Friday, April 13, 2018 3:12 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] Re: Exterior Play Area
Yeah I didn't think you meant tire storage for real but some are making
suggestions based on some assumptions of what wil
rum@lists.firesprinkler.org
>Cc: sprinklerforum@lists.firesprinkler.org
>Subject: RE: [EXTERNAL] Re: Exterior Play Area
>
>I'm not sure assuming the worst is the way to go. Additionally, 2/3 of
>the covered area is concrete basketball court.
>John Irwin
>DynaFire Inc.
>Ta
@lists.firesprinkler.org
Subject: RE: [EXTERNAL] Re: Exterior Play Area
I'm not sure assuming the worst is the way to go. Additionally, 2/3 of the
covered area is concrete basketball court.
John Irwin
DynaFire Inc.
Tampa Fire Sprinkler Division
727-282-9243
This email was sent from a mobile device. Please fo
; fire load, there is one).
>>>>
>>>> So once again, from the top: NFPA 13 doesn't exclude this area
>>>> because it's occupied and has or potentially has combustibles
>>>> below it. The building code defines it as a building. Why don't
sprinkler.org] On Behalf
Of bcasterl...@fsc-inc.com
Sent: Friday, April 13, 2018 12:10 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Exterior Play Area
I vote no sprinklers required -- open and noncombustible- the
rockinghorse on a spring is like a newspaper machine - there will
always be
building. Why don't we have to sprinkler it?
>>
>> Steve
>>
>>
>>
>> -Original Message-----
>> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
>> On Behalf Of bcasterl...@fsc-inc.com
>> Sent: Friday
y
word for it - go look it up in the IBC.This is a building.
SML
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of bcasterl...@fsc-inc.com
Sent: Friday, April 13, 2018 2:07 PM
To: sprinklerforum@lists.firesprinkler.org
Subj
lding. Why don't we have
to sprinkler it?
Steve
-Original Message-
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
bcasterl...@fsc-inc.com
Sent: Friday, April 13, 2018 12:10 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: E
iresprinkler.org] On
Behalf Of bcasterl...@fsc-inc.com
Sent: Friday, April 13, 2018 12:10 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Exterior Play Area
I vote no sprinklers required -- open and noncombustible- the rockinghorse on a
spring is like a newspaper machine - there wil
l Message-
>From: Sprinklerforum
>[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
>bcasterl...@fsc-inc.com
>Sent: Friday, April 13, 2018 12:10 PM
>To: sprinklerforum@lists.firesprinkler.org
>Subject: [EXTERNAL] Re: Exterior Play Area
>
>I vote no sprinklers
essage-
> From: Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
> bcasterl...@fsc-inc.com
> Sent: Friday, April 13, 2018 12:10 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: [EXTERNAL] Re: Exterior Play Area
>
> I vote no sprinkler
-inc.com
Sent: Friday, April 13, 2018 12:10 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: [EXTERNAL] Re: Exterior Play Area
I vote no sprinklers required -- open and noncombustible- the rockinghorse on a
spring is like a newspaper machine - there will always be just one of them- not
one today
...@lists.firesprinkler.org] On Behalf Of
John Irwin
Sent: Friday, April 13, 2018 11:10 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Exterior Play Area
I can appreciate your opinion, but I need a code reference. 😉
John Irwin
DynaFire Inc. – “Same Day – Next Day”
From: Sprinklerforum
8.15.7.5.
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of John Irwin
Sent: Friday, April 13, 2018 11:10 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Exterior Play Area
I can appreciate your opinion, but I need a code reference. 😉
John
I can appreciate your opinion, but I need a code reference. 😉
John Irwin
DynaFire Inc. – “*Same Day – Next Day*”
*From:* Sprinklerforum *On
Behalf Of *Steve Leyton
*Sent:* Friday, April 13, 2018 1:47 PM
*To:* sprinklerforum@lists.firesprinkler.org
*Subject:* RE: Exterior Play Area
Assuming there’s play equipment there (fire load) and knowing that there are
kids occupying the space, I wouldn’t call this an “exterior projection”. It’s
a shad structure with occupancy below and IMO requires sprinkler protection.
SML
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists
27 matches
Mail list logo