RE: Fire pump annual test

2012-10-08 Thread George Church
, 2012 8:19 PM To: sprinklerforum@firesprinkler.org Subject: Re: Fire pump annual test on 2nd thought (calc), 65-70% is closer, I bet. 78% is 4500 @ 170. by the way, what does PLD stand for? Quoting bcasterl...@fsc-inc.com: > George, > 78% efficient at overload.. not too shabby! > Do y

Re: Fire pump annual test

2012-10-06 Thread MPhelps
Power Limiting Device (aka Cruise Control) - Original Message - From: bcasterl...@fsc-inc.com [mailto:bcasterl...@fsc-inc.com] Sent: Sunday, October 07, 2012 12:18 AM To: sprinklerforum@firesprinkler.org Subject: Re: Fire pump annual test on 2nd thought (calc), 65-70% is closer, I bet

Re: Fire pump annual test

2012-10-06 Thread bcasterline
on 2nd thought (calc), 65-70% is closer, I bet. 78% is 4500 @ 170. by the way, what does PLD stand for? Quoting bcasterl...@fsc-inc.com: George, 78% efficient at overload.. not too shabby! Do you recall the rated RPM? If I assume a 14" impeller diam. I get 2600 RPM. I thought about converting t

Re: Fire pump annual test

2012-10-06 Thread bcasterline
George, 78% efficient at overload.. not too shabby! Do you recall the rated RPM? If I assume a 14" impeller diam. I get 2600 RPM. I thought about converting the 400 speed reduction to the pump room temperature rise but said nahhh.. it would be negligible against the 1st law of testosterone, Lo

RE: Fire pump annual test

2012-10-04 Thread George Church
Sent: Wednesday, October 03, 2012 2:09 PM To: sprinklerforum@firesprinkler.org Subject: Re: Fire pump annual test When testing a fire pump, pump speed ALWAYS drops with increased flow. In a message dated 10/3/2012 8:43:56 A.M. Eastern Daylight Time, bcasterl...@fsc-inc.com writes: Tom, let

Re: Fire pump annual test

2012-10-03 Thread bcasterline
thanks DJJ8389, that's what I thought. I guess electric motor drive is more consistent and closer to expectations than engine driven. As far as Tom's 'adjusting the pressure to rated speed' goes though, with electric we are at the mercy of the local Power and Light, whereas with engine driv

Re: Fire pump annual test

2012-10-03 Thread DJJ8389
, mid- November in Kansas :) -Original Message- From: bcasterl...@fsc-inc.com [mailto:bcasterl...@fsc-inc.com] Sent: Wednesday, October 03, 2012 5:30 AM To: sprinklerforum@firesprinkler.org Subject: RE: Fire pump annual test Tom, I guess once we equate what goes out of the tachometer wi

RE: Fire pump annual test

2012-10-03 Thread Brad Casterline
resprinkler.org Subject: RE: Fire pump annual test Tom, I guess once we equate what goes out of the tachometer with what goes into the thermometer, the speed does not change-- the magic of the second law of thermodynamics! (or, as you put it-- 'Pump affinity'). Quoting Tom Duross : &g

RE: Fire pump annual test (VALVES)

2012-10-03 Thread Matthew J. Willis
...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Tom Duross Sent: Tuesday, October 02, 2012 7:15 PM To: sprinklerforum@firesprinkler.org Subject: RE: Fire pump annual test (VALVES) I would never put full pump pressure on a header that's normally empty or use hose

RE: Fire pump annual test

2012-10-03 Thread bcasterline
Tom, I guess once we equate what goes out of the tachometer with what goes into the thermometer, the speed does not change-- the magic of the second law of thermodynamics! (or, as you put it-- 'Pump affinity'). Quoting Tom Duross : Brad, we measure rpm as a means of adjusting pressures to ra

Re: Fire pump annual test (VALVES)

2012-10-02 Thread Timothy W Goins
Some UL/FM playpipes are listed with and without the tips. I used to have a listed " test nozzle also. "For I am not ashamed of the gospel , , because it is God’s power for salvation to everyone who believes..." HCS Romans 1:16 On Oct 2, 2012, at 6:14 PM, "Tom Duross" wrote: > This message c

RE: Fire pump annual test

2012-10-02 Thread Tom Duross
after the increaser). -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brad Casterline Sent: Tuesday, October 02, 2012 9:02 AM To: sprinklerforum@firesprinkler.org Subject: RE: Fire pump annual test Gerzayn, It

RE: Fire pump annual test (VALVES)

2012-10-02 Thread Tom Duross
I would never put full pump pressure on a header that's normally empty or use hose gates to modulate either. Always modulate with the OS&Y or BV, keep the pump pressure in the system, who cares if you have 2) 18's, a 19 and a 17? Playpipes are only listed with the tips on (1-1/8") which is why we

RE: Fire pump annual test (VALVES)

2012-10-02 Thread Matthew J. Willis
ouncing of the gauge in use) R/ Matt -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Cahill, Christopher Sent: Tuesday, October 02, 2012 11:12 AM To: sprinklerforum@firesprinkler.org Subject: RE: Fire pump a

RE: Fire pump annual test (VALVES)

2012-10-02 Thread Cahill, Christopher
J. Willis Sent: Tuesday, October 02, 2012 9:59 AM To: sprinklerforum@firesprinkler.org Subject: RE: Fire pump annual test (VALVES) ". If you have the same setup on each valve and playpipe you can open all the 2.5" valves first with no flow and throttle with the manifold valve as all the

RE: Fire pump annual test (VALVES)

2012-10-02 Thread Matthew J. Willis
". If you have the same setup on each valve and playpipe you can open all the 2.5" valves first with no flow and throttle with the manifold valve as all the playpipes should be the same. " Unless your manifold valve is non-throttling (OS&Y). Even then, isn't each hose lay different? R/ Matt

RE: Fire pump annual test

2012-10-02 Thread Hinson, Ryan
rg Subject: RE: Fire pump annual test Gerzayn, It is OK to do more, but the minimum required is to read/record (4) things at (3) flow rates. The (3) flow rates are 0, rated, and 150% rated. The (4) things are: 1. The difference between suction pressure and discharge pressure 2. RPM 3. Vol

RE: Fire pump annual test

2012-10-02 Thread Cahill, Christopher
One clarification. You can't take your final pressure pitot readings until you have all the valves/playpipes open. As you open subsequent ones the prior ones drop a bit. Your best bet is BEFORE you do the test know what pitot you want from each playpipe and how many valves you want open. Ope

RE: Fire pump annual test

2012-10-02 Thread Brad Casterline
Gerzayn, It is OK to do more, but the minimum required is to read/record (4) things at (3) flow rates. The (3) flow rates are 0, rated, and 150% rated. The (4) things are: 1. The difference between suction pressure and discharge pressure 2. RPM 3. Volts 4. Amps The following is FYI for sprinkler