Re: Sprinkler drop sizing

2021-07-01 Thread Mark Phillips via Sprinklerforum
Code allows you to retrofit that with a 1/2 x1 ell and a 1 “ new drop if the outlets are 1/2” off line Could you elaborate? Sent from my mobile device Please excuse spelling, grammar, and auto correction. Mark Phillips Branch Manager Fire Sprinkler Design, Install, Inspections Service, Backflows

RE: Sprinkler drop sizing

2021-07-01 Thread Jennifer Cornett via Sprinklerforum
rg Cc: Jennifer Cornett Subject: Re: Sprinkler drop sizing Code allows you to retrofit that with a 1/2 x1 ell and a 1 " new drop if the outlets are 1/2" off line Could you elaborate? Sent from my mobile device Please excuse spelling, grammar, and auto correction. Mark Phillips

RE: Sprinkler drop sizing

2021-07-01 Thread Dennis Wilson via Sprinklerforum
ler.org Cc: Jennifer Cornett Subject: RE: Sprinkler drop sizing The branchlines are 1", 1-1/4", etc. with a tee and the drop is ½" pipe to the sprinkler heads. Where I would normally design a 1" drop, they used ½". Sincerely, Jennifer Cornett, NICET SET Sprinkler Sales Firetro

Re: Sprinkler drop sizing

2021-07-01 Thread 321 via Sprinklerforum
I think 13 tells us in a round about way that 1/2" and 3/4" steel can only be used as "Pilot Line" detector piping per Chapter 8 and Chapter 6. Look at Note "B" in the allowed pipe size table in Chapter 6...it sends you to the pilot line section in Chapter 8 and restricts those sizes to that use

RE: Sprinkler drop sizing

2021-07-01 Thread Ed Kramer via Sprinklerforum
prinklerforum@lists.firesprinkler.org Cc: Jennifer Cornett Subject: RE: Sprinkler drop sizing The branchlines are 1", 1-1/4", etc. with a tee and the drop is ½" pipe to the sprinkler heads. Where I would normally design a 1" drop, they used ½". Sincerely, Jennifer Corne

RE: Sprinkler drop sizing

2021-07-02 Thread Jennifer Cornett via Sprinklerforum
name.  Thank you. -Original Message- From: Dennis Wilson Sent: Thursday, July 1, 2021 10:55 AM To: sprinklerforum@lists.firesprinkler.org; Mark Phillips Cc: Jennifer Cornett Subject: RE: Sprinkler drop sizing I have the 1985 book, and it wasn't allowed then. Same rule as now, ½

Re: Sprinkler drop sizing

2021-07-06 Thread John Denhardt via Sprinklerforum
7;s name. Thank you. > > > > > > > -Original Message- > From: Dennis Wilson > Sent: Thursday, July 1, 2021 10:55 AM > To: sprinklerforum@lists.firesprinkler.org; Mark Phillips < > philli...@pyebarkerfire.com> > Cc: Jennifer Cornett > Su