Thanks, that's what I thought.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve
Leyton
Sent: Thursday, October 27, 2011 9:26 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: UG pipe to remote FD
We spec C-900 (Class 200) for remote FDC's, and those portions of fire
service laterals downstream of FDC's, as a regular practice.
Steve Leyton
Protection Design & Consulting
Dewayne Martinez wrote:
Can PVC pipe used in water mains be used for the underground pipe for a
remote FDC connection?
inkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Aaron Peck
Sent: Thursday, October 27, 2011 10:04 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: UG pipe to remote FDC
Well I don't have a code book in front of me but I don't believe it can be.
Because of the pressure rati
Well I don't have a code book in front of me but I don't believe it can be.
Because of the pressure rating. Now if the check valve is not at the FDC but
inside the building perhaps that's acceptable.
Because when the fire department pumps in to it, I'm not exactly sure, but the
pressures should