I need some help with a seismic problem.
I am making modifications to a 1970's sprinkler system in NC, we are using the
2000 ed of NFPA 13.
There is no seismic bracing on this system.
I have had to add some new main in various areas.
The local AHJ is requiring that only the new sprinkler
In a 13R building there are a 2" cpvc blazemaster supply mains run to
supply the upper floor sprinkler systems. The piping will be supported
using 2" long rods. The location requires seismic protection. Will sway
bracing be required? Any other requirements?
Thanks,
Tony
__
Quick question regarding seismic bracing. What is the consensus with regard
to the 40' & 80' spacing, do you take this as accumulative or do you start
over each time the main has an elbow or change of direction in it? For
example: if you have a main that runs 30' horizontal th
Hello Sprinklerforum,
I am looking for ways to put longitudinal bracing on a straight run of 6"
Schedule 40 pipe that can expand or contract About 5" with a temperature swing
from 40 degrees to 100 degrees. This is a 1400' durn near straight run. I am
looking at using a Metraflex Building Sep
Forum,
When spacing braces I was taught that you can include directional changes in
the pipe as long as you stay within the 40-80 ft. rule. For example: if
there is 15' of pipe, then 90 elbow with 5' of pipe, then another 90 with 10
ft. of pipe (total linear ft is 30) you can have braces at each en
Is it possible to have a Main that only has Lateral Bracing & no Longitudinal
Bracing? Say you have a Main that is 40'-0" long and have a Lateral brace
within 6' of each end, are you required to have a Longitudinal brace in the
middle?
Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssy
11:17 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: FW: Seismic Bracing
Is it possible to have a Main that only has Lateral Bracing & no
Longitudinal Bracing? Say you have a Main that is 40'-0" long and have a
Lateral brace within 6' of each end, are you required to
Steve
Leyton
Sent: Tuesday, January 07, 2014 1:27 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Seismic Bracing
I believe that you need at least one longitudinal brace in the scenario you
describe.
Steve Leyton
-Original Message-
From: sprinklerforum-boun
M
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Seismic Bracing
Yes, you need a longitudinal brace as Steve said. Lateral braces can act as
longitudinal braces if they are within 24 in. of the pipe braced
longitudinally and the brace is on a pipe of equal or greater size than the
pipe being b
Seismic design category C, contractor submittal package,
Do you provide a calc sheet for EQ bracing or just locate per NFPA 13 and send
typical catalog data sheets?
FM Global project, BTW.
Craig L. Prahl, CET
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spart
g the
2000 ed of NFPA 13.
There is no seismic bracing on this system.
I have had to add some new main in various areas.
The local AHJ is requiring that only the new sprinkler main will need to be
braced.
Does anyone know if this is an actual standards requirement or just a
preference of the loca
Of Forest Wilson
Sent: Friday, September 05, 2014 8:15 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Seismic bracing
Does the building code require it?
The building code dictates if you are in a seismic zone and NFPA 13 tells you
how to do it.
On 9/5/2014 8:13 AM, Steve Sorrell
nklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Steve Sorrell
Sent: Friday, September 05, 2014 8:20 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Seismic bracing
The building code requires it.
How effective would a partially braced system be, only th
The AHJ can't just "require it". His preference is not relevant. Also seismic
bracing is not based on Zones or Maps anymore, hasn't been for quite a while.
I'm curious why you're using the 2000 edition of NFPA 13.
Anyway back to seismic.
Seismic requirements ar
@lists.firesprinkler.org
Subject: RE: Seismic bracing
The AHJ can't just "require it". His preference is not relevant. Also
seismic bracing is not based on Zones or Maps anymore, hasn't been for quite
a while.
I'm curious why you're using the 2000 edition of NFPA 13.
An
Check the structural notes. If it is seismic design category a or b, then no
seismic. If SDC of C or higher then bracing required.
It seems odd to do seismic bracing of piping if the building is not designed to
resist seismic forces.
Travis Mack, SET
MFP Design, LLC
Sent from my iPhone
9:11 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Seismic bracing
Check the structural notes. If it is seismic design category a or b, then no
seismic. If SDC of C or higher then bracing required.
It seems odd to do seismic bracing of piping if the building is not designed to
resi
nklerforum@lists.firesprinkler.org
Subject: RE: Seismic bracing
The AHJ can't just "require it". His preference is not relevant. Also seismic
bracing is not based on Zones or Maps anymore, hasn't been for quite a while.
I'm curious why you're using the 2000 edition of NF
ehalf Of Steve Sorrell
Sent: Friday, September 05, 2014 8:13 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Seismic bracing
I need some help with a seismic problem.
I am making modifications to a 1970's sprinkler system in NC, we are using
the 2000 ed of NFPA 13.
There is no seismic b
Stephen,
I don't believe the AHJ you're dealing with has thought this
decision through very carefully. They seem to be equating "seismic
bracing" with "seismic protection", which includes such other features
as flexible couplings, clearance requirements,
Brooks
Sent: Friday, September 05, 2014 10:09 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Seismic bracing
"Does anyone know if this is an actual standards requirement or just a
preference of the local AHJ ?"
One way to do this would be to ask the AHJ. This is something
e past and have little to no meaning anymore. I
can have two buildings 50 ft apart and one require seismic bracing and one not
require it. The factors determining that are not difficult to maneuver through
but take some knowledge of the Building Code and hazards present, building use,
soil
t: Friday, September 05, 2014 5:11 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Seismic bracing
Stephen,
I don't believe the AHJ you're dealing with has thought this decision
through very carefully. They seem to be equating "seismic bracing" with
"s
ooperation.
-Original Message-
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
rfletc...@aerofire.com
Sent: Friday, September 05, 2014 11:16 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Seismic bracing
Some jurisdictions around here re
I have never had an AHJ in either CT or MA ask for calcs for seismic bracing.
Most just want to see something.
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)
> On Sep 5, 2014, at 11:10 AM, wrote:
>
> Some jurisdictions around her
Oh boy, here we go again. Every time the subject of seismic bracing /
protection comes up, it shows that there is a general lack of understanding
among contractors and designers (myself included) as to when it is required,
what is required, and how to do it correctly.
We need more education
il:tm...@mfpdesign.com
On 9/5/2014 8:58 AM, wmens...@comcast.net wrote:
Oh boy, here we go again. Every time the subject of seismic bracing /
protection comes up, it shows that there is a general lack of understanding
among contractors and designers (myself included) as to when it is required,
wh
-boun...@lists.firesprinkler.org] On
Behalf Of Jim Davidson
Sent: Friday, September 05, 2014 8:43 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Seismic bracing
Ron,
I hope you have a hold harmless letter from the building owner and or developer
because the sprinkler contractor will b
ismic bracing
Oh boy, here we go again. Every time the subject of seismic bracing /
protection comes up, it shows that there is a general lack of understanding
among contractors and designers (myself included) as to when it is required,
what is required, and how to do it correctly.
We need
forum-boun...@lists.firesprinkler.org] On
Behalf Of wmens...@comcast.net
Sent: Friday, September 05, 2014 11:58 AM
To: sprinklerforum
Subject: Re: Seismic bracing
Oh boy, here we go again. Every time the subject of seismic bracing /
protection comes up, it shows that there is a general lack of und
u for your cooperation.
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of wmens...@comcast.net
Sent: Friday, September 05, 2014 12:16 PM
To: sprinklerforum
Subject: Re: Seismic bracing
Oh boy, here we go again. Every time the su
--Original Message-
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of wmens...@comcast.net
> Sent: Friday, September 05, 2014 11:58 AM
> To: sprinklerforum
> Subject: Re: Seismic bracing
>
>
>
> Oh boy, here we go again. Eve
f Jim Davidson
Sent: Friday, September 05, 2014 9:28 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Seismic bracing
The seismic design classification should be determined by the structural
engineer who determines the SDC of the site. Once the SDC is determined then
you can go into e
014 List of 100 Best Companies to Work For
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of rfletc...@aerofire.com
Sent: Friday, September 05, 2014 12:34 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Seismic bracing
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of rfletc...@aerofire.com
Sent: Friday, September 05, 2014 1:46 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Seismic bracing
Since it is an existing building I doubt any of the things you have listed will
be done. I guess I
: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of rfletc...@aerofire.com
Sent: Friday, September 05, 2014 12:34 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Seismic bracing
Since it is an existing building I doubt any of the things you have listed
:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
rfletc...@aerofire.com
Sent: Friday, September 05, 2014 12:34 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Seismic bracing
Since it is an existing building I doubt any of the things you have
listed will be done. I gue
Short rods only eliminate lateral bracing. You will still need
longitudinal bracing.
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/9221841
erforum-boun...@lists.firesprinkler.org]
On Behalf Of Travis Mack, SET
Sent: Monday, March 20, 2017 12:41 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Seismic Bracing
Short rods only eliminate lateral bracing. You will still need longitudinal
bracing.
Travis Mack, SET
MFP Design
Rocci,
You're correct in one way, the '16 edition no longer allows the
use of hanger rods less than 6" long to omit lateral seismic bracing on
mains, if the Cp value is greater than 0.50. That does indeed cover
most of California, and several other places as well.
7;16 edition no longer allows the use
> of hanger rods less than 6" long to omit lateral seismic bracing on mains,
> if the Cp value is greater than 0.50. That does indeed cover most of
> California, and several other places as well.
> That change was added to 9.3.5.5.10.2, (4) in th
;> Rocci,
>> You're correct in one way, the '16 edition no longer allows the use of
>> hanger rods less than 6" long to omit lateral seismic bracing on mains, if
>> the Cp value is greater than 0.50. That does indeed cover most of
>> California, an
te:
Rocci,
You're correct in one way, the '16 edition no longer allows
the use of hanger rods less than 6" long to omit lateral seismic
bracing on mains, if the Cp value is greater than 0.50. That
does indeed cover most of California, and several other places
Hi,
I manage a 1970 vintage concrete tilt-up industrial park with a panelized
roof in Southern California. As part of my 5-yr, my contractor is telling
me that I need to install seismic clips on some of the locations where the
pipes traverse a hanger (v-hangers, in this case).
I am looking for i
Larry:
Seismic bracing requirements have tightene up a lot since the 1970's for
fire sprinklers. Bracing was often referred to as the weakest aspect of a
sprinkler system prior to the turn of the century. You can probably
find a copy of NFPA 13 (Sprinkler Installation Standard) at your
: Seismic Bracing
Quick question regarding seismic bracing. What is the consensus with
regard
to the 40' & 80' spacing, do you take this as accumulative or do you
start
over each time the main has an elbow or change of direction in it? For
example: if you have a main that runs 30' hor
Brian
Harris
Sent: Monday, March 21, 2011 7:46 AM
To: sprinklerforum@firesprinkler.org
Subject: Seismic Bracing
Quick question regarding seismic bracing. What is the consensus with
regard
to the 40' & 80' spacing, do you take this as accumulative or do you
start
over each time the main has
ve
>
>
> -Original Message-
> From: sprinklerforum-boun...@firesprinkler.org
> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian
> Harris
> Sent: Monday, March 21, 2011 7:46 AM
> To: sprinklerforum@firesprinkler.org
> Subject: Seismic Bracing
>
>
.
Roland
On Mar 21, 2011, at 7:45 AM, Brian Harris wrote:
Quick question regarding seismic bracing. What is the consensus with
regard
to the 40' & 80' spacing, do you take this as accumulative or do you
start
over each time the main has an elbow or change of direction in it? F
looks like it did not like my copy and paste. Go look at the ROP:
13-338 and 341
Roland
On Mar 22, 2011, at 8:22 AM, Roland Huggins wrote:
The TC just added at the ROP meeting the following:
-- next part --
The same issue on hangers has been addressed as 13-327 w
1400' of 6" 40! Ouch, my back...
Hello Sprinklerforum,
I am looking for ways to put longitudinal bracing on a straight run of 6"
Schedule 40 pipe that can expand or contract About 5" with a temperature
swing from 40 degrees to 100 degrees. This is a 1400' durn near straight
run. I am looking
Expansion joint? Maybe less expensive than Metra Flex.
George Medina Jr.
Sr. Fire Sprinkler Designer
-Original Message-
From: Coastal
To: sprinklerforum@firesprinkler.org
Sent: Thu, Jul 1, 2010 3:57 pm
Subject: Seismic Bracing
Hello Sprinklerforum,
I am looking for ways to
This may be a good application for cable bracing. Contact Loos Co.
(www.earthquakebrace.com) and pose the question to them.
At 06:57 PM 7/1/2010, you wrote:
>Hello Sprinklerforum,
>
> I am looking for ways to put longitudinal bracing on a straight
> run of 6" Schedule 40 pipe that can expand
If this is new construction, ask the structural engineer how much the
structure expands and contracts with the temperature swings. If it's
similar, then you may not need to be concerned about expansion - your pipe
and the structure would expand/contract as a unit. Just install
longitudinal braces
It's also relevant to note that if a seismic separation assembly is
installed, a four-way brace within 6'-0" of either side of that assembly
will be required according to 9.3.3 of -13.
--
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
parsleyconsult...@cox.net
07/01/2010 05:57 PM
Subj
I know this was discussed recently but I don't think this specific point
was brought up. Currently there is only one listed sway brace for CPVC and
it is a lateral brace. Now in order to provide longitudinal bracing it was
suggested to install a lateral brace on the branch line within 24 in. of
the
I have a situation where I have a main elevation of 27'-0 and ceilings @
9'-0, this creates single 1"x16'-0 drops w/threaded couplings and then a
flexible drop to ceiling. The whole reason for keeping the main high is that
it would be impossible to seismic brace. In reviewing NFPA-13 2007 I only
se
As you already know, 13 does not explicitly address this issue (at
least not that I could find in a quick search of my memory and the
text). The question I have is since the load calculation for the
lateral brace is based upon the perpendicular load but after an elbow
the same plane become
Longitudinal brace within 24" of the 5' piece can act as its lateral.
Lateral brace within 24" of the 5' piece can act as its longitudinal.
Otherwise, you have to have both a lateral and longitudinal on the 5' piece.
Scott Mitchell
Brian Harris <[EMAIL PROTECTED]> wrote:
Forum,
W
When preparing an estimate for bid how do most factor in costs for EQ bracing
and engineering?
Is it a percentage or based on a preliminary layout or
Off-line responses are welcome if you don't want to post your trade secrets.
All responses are kept confidential for the right price. ;)
Brian,
There is no option in NFPA 13 which allows omission of longitudinal
bracing. In the scenario you describe, the 40' long main would indeed
require a longitudinal brace,and any location along the length of that
main would be acceptable, as it must be no more than 40' from the end of
the
Sent: Tuesday, January 07, 2014 2:31 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: FW: Seismic Bracing
Brian,
There is no option in NFPA 13 which allows omission of longitudinal bracing.
In the scenario you describe, the 40' long main would indeed require a
longitudinal brace,and an
@lists.firesprinkler.org
Subject: seismic bracing calcs
Seismic design category C, contractor submittal package,
Do you provide a calc sheet for EQ bracing or just locate per NFPA 13 and send
typical catalog data sheets?
FM Global project, BTW.
Craig L. Prahl, CET
Fire Protection Group Lead
There really is no locate per NFPA 13. You still have max of 40/80, 4 way at
change in direction and laterals no more than 6' from end of cross main. But,
with all of the other requirements in chapter 9, you must calculate the bracing
spacing.
I consider it just like pipe sizing calcs any more
fire-design.com
www.fire-design.com
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Thursday, February 20, 2014 7:27 AM
To: sprinklerforum@lists.firesprinkler.org
Subject
rforum-boun...@lists.firesprinkler.org
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
> craig.pr...@ch2m.com
> Sent: Thursday, February 20, 2014 7:27 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: seismic bracing calcs
>
> Seismic design category
o, SET CFPS
520.971.2322 Cell
Skype: steven.scandaliato
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
rongreenman .
Sent: Thursday, February 20, 2014 9:41 AM
To: sprinklerforum@lists.firesprinkler.org
arris
Sent: Thursday, February 20, 2014 6:32 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: seismic bracing calcs
Both...
Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum
ts.firesprinkler.org] On Behalf Of
> Brian Harris
> Sent: Thursday, February 20, 2014 6:32 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: seismic bracing calcs
>
> Both...
>
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
>
> -Original
nklerforum-boun...@lists.firesprinkler.org] On Behalf Of
rongreenman .
Sent: Thursday, February 20, 2014 10:36 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: seismic bracing calcs
>From the Piemontesi to the greasy Sicilian, with molte amore. I won't hold
it against you that your family is from the
half Of
> rongreenman .
> Sent: Thursday, February 20, 2014 10:36 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: seismic bracing calcs
>
> From the Piemontesi to the greasy Sicilian, with molte amore. I won't hold
> it against you that your family is from the
lf Of
Steven Scandaliato
Sent: Thursday, February 20, 2014 8:46 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: seismic bracing calcs
Hey...you don't want to mess with us...cause god knows...we have
"friends"everywhere!
Steven Scandaliato, SET CFPS
520.971.2322 Cell
Skype
to:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
> Steven Scandaliato
> Sent: Thursday, February 20, 2014 8:46 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: seismic bracing calcs
>
> Hey...you don't want to mess with us...cause god kno
: seismic bracing calcs
Since Greenman is pure mongrel (and occasionally junkyard mongrel), apart from
being anglicized Gaelic, and the other half is Ferracone.
And since I messed up my leg I keep tripping over my fingers, Mr. Noytel.
Then there's also the aixelsyd
On Thu, Feb 20, 2014 at
sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steven
Scandaliato
Sent: Thursday, February 20, 2014 11:00 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: seismic bracing calcs
Wait...hold on...just to make sure, and
sprinkler.org] On Behalf Of Steven
> Scandaliato
> Sent: Thursday, February 20, 2014 11:00 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: seismic bracing calcs
>
> Wait...hold on...just to make sure, and Craig I am sure you probably know
> this...BUT we have a
-boun...@lists.firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Thursday, February 20, 2014 11:37 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: seismic bracing calcs
Steven,
I have never received a contractor shop drawing that covered things to the
detail you describe. It'
...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve
Leyton
Sent: Thursday, February 20, 2014 4:45 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: seismic bracing calcs
And we haven't gotten approval for a document set without including all of
those thin
t: RE: seismic bracing calcs
I have specified the shop drawings and bracing calculations be submitted to the
project structural engineer to confirm the adequacy of the attachment point to
resist the loading. Is this a common practice?
Bill Brooks
-Original Message-
From: sprinklerforum
2
craig.pr...@ch2m.com
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
rongreenman .
Sent: Thursday, February 20, 2014 4:33 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: seismic bracing
pipe size then we got way bigger
problems than seismic features...
Sent from my BlackBerry 10 smartphone.
From: craig.pr...@ch2m.com
Sent: Thursday, February 20, 2014 4:04 PM
To: sprinklerforum@lists.firesprinkler.org
Reply To: sprinklerforum@lists.firesprinkler.org
Subject: RE: seismic bracing
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
Steven Scandaliato
Sent: Thursday, February 20, 2014 2:13 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: seismic bracing calcs
Well that's were we are going to di
inkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steven
Scandaliato
Sent: Thursday, February 20, 2014 5:13 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: seismic bracing calcs
Well that's were we are going to disagree...I haven't put tick marks on a d
inkler.org] On Behalf Of Steven
> Scandaliato
> Sent: Thursday, February 20, 2014 5:13 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: seismic bracing calcs
>
> Well that's were we are going to disagree...I haven't put tick marks on a
> dwg or required them on a dwg s
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
rongreenman .
Sent: Thursday, February 20, 2014 3:30 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: seismic bracing calcs
I think the standard
cannot be
guaranteed on the Internet.
Original message
From: "rongreenman ."
Date:02/20/2014 11:36 AM (GMT-05:00)
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: seismic bracing calcs
From the Piemontesi to the greasy Sicilian, with molte amore. I won
ity and security
> of this message cannot be guaranteed on the Internet.
>
> Original message
> From: "rongreenman ."
> Date:02/20/2014 11:36 AM (GMT-05:00)
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: seismic bracing calcs
>
> Fro
lose its contents to
>> anyone. Please send us by fax any message containing deadlines as incoming
>> e-mails are not screened for response deadlines. The integrity and security
>> of this message cannot be guaranteed on the Internet.
>>
>> Original message ---
them and the time to install them, ... We should at least do them right.
My two cents.
Sent from my Verizon Wireless 4G LTE smartphone
Original message
From: "rongreenman ."
Date:02/20/2014 10:12 PM (GMT-07:00)
To: sprinklerforum@lists.firesprinkler.org
Subj
nkler.org] On Behalf Of
rongreenman .
Sent: Friday, February 21, 2014 12:13 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: seismic bracing calcs
How do you locate per 13? How do you know what you did will work? How do you
know that 1" x 34" brace at 37 degrees to side of a b
-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steven
Scandaliato
Sent: Thursday, February 20, 2014 5:13 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: seismic bracing calcs
Well that's were we are goi
ot an adequate degree of diligence, IMHO
Oops, my soapbox just broke.
Steve Leyton
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
John Denhardt
Sent: Friday, February 21, 2014 9:12 AM
14 8:14 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: seismic bracing calcs
Exactly. Unless your drawing which shows those little criss-cross arrows
are accompanied by calculations AND unless your calculations are acceptable
to the project structural engineer, then you do not have a comple
.2322 Cell
> Skype: steven.scandaliato
>
>
> -Original Message-
> From: sprinklerforum-boun...@lists.firesprinkler.org
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Bill
> Brooks
> Sent: Friday, February 21, 2014 8:14 AM
> To: sprinklerforum@list
r.org
Subject: RE: seismic bracing calcs
This goes to perpetuate the notion that we're different or special and
that's good and okay. I respectfully disagree - it's not.
Every other discipline is required to structurally engineer their supports,
coordinate loads and attachme
ssage-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
rfletc...@aerofire.com
Sent: Friday, February 21, 2014 10:18 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: seismic bracing calcs
I think the reason we are s
firesprinkler.org
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve
> Leyton
> Sent: Friday, February 21, 2014 10:27 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: seismic bracing calcs
>
> This goes to perpetuate the notion that we're
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
Todd - Work
Sent: Friday, February 21, 2014 1:21 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: seismic bracing calcs
I think you also need to take into account reg
.@lists.firesprinkler.org] On Behalf Of
> Todd - Work
> Sent: Friday, February 21, 2014 1:21 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: seismic bracing calcs
>
> I think you also need to take into account regional differences. Some
> areas, like Leytonland, have a