Look at 8.15.6 which says when you do not have to protect. Don’t forget that
if you are able to omit, you still have to address the 3000 sf remote area
(11.2.3.1.5.1) which includes 8.15.6 in the bounding paragraph. It was added
back in the 2010 ed.
Roland
Roland Huggins, PE - Senior VP Engi
If only 2 ft, you would need concealed space sprinklers. Use their spacing
requirements
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
Office: 860-535-2080 Cell: 860-608-4559 [tel:860-608-4559] Fax:
860-553-3553
On Tue, Feb 14, 2017 at 8:39 AM, Mark Phillips
wrote:
Mor
Morning everyone
My gut is telling me I need to add heads under new platforms but I could use
some reassurance / conformation.
I have a situation where a church constructed of Type VB wants to add a
mechanical room above an existing area in its attic space.
The space will be approximately 3 f