RE: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-23 Thread Stephen Cooke
so need to be considered, and also if the building is effectively vented as discussed else where. From: jedrothw...@gmail.com Date: Sat, 21 May 2016 20:09:44 -0400 Subject: Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal To: vortex-l@eskimo.com

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Lennart Thornros
Jed, if I understand you right the world is full of idiots and scammers and potential jailbirds. All technical skepticism you have been provided are done by people without common sense. You obviously have more information than anyone else (only from IH?) and that means your opinion is the one that

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Jed Rothwell
Alan Fletcher wrote: I accept your claim that 1MW in an un-ventilated, insulated room would be > fatal. > > But that is not the case : a 30,000 CPM is sufficient to ventilate it, and > there is a fan (of similar dimensions to one particular example) on the > roof. (Plus convective loss, which wou

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Alan Fletcher
ssi's" man. From: "Jed Rothwell" To: "vortex-l" Sent: Saturday, May 21, 2016 3:11:49 PM Subject: Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal a.ashfield < a.ashfi...@verizon.net > wrote: Your cl

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Jed Rothwell
Alan Fletcher wrote: The point is that this thread's title : "1 MW of heat in a 6,500 sq. ft. > facility without industrial ventilation would be fatal" is false. > Are you saying this would not be true? Are you saying that putting 25 heaters into an enclosed room with no fan, turning them on wit

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Jed Rothwell
a.ashfield wrote: > Your claim that the heat released from the 1 MW plant would be fatal has > been shot down. > That was not my claim. You are making a straw-man argument. My claim was that without industrial grade ventilation, when you heat a space with 26 times more heat than is normally us

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread a.ashfield
Jed, Your claim that the heat released from the 1 MW plant would be fatal has been shot down. Likewise, your certainty of fraud because Rossi was the one who prevented IH from visiting the customer. Your other evidence of fraud seem to come mainly from what IH has told you. Before accepting

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Alan Fletcher
The point is that this thread's title : "1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal" is false. On the contract point, re-read the IH/Rossi contract https://animpossibleinvention.files.wordpress.com/2016/04/rossi_et_al_v_darden_et_al__flsdce-16-21199__

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Jed Rothwell
Alan Fletcher wrote: The roof has one circular roof fan at the left, and a rectangular box at > the other. > I believe the box on the right is a skylight window. We are talking about this photo, which I think was taken in 2014. That's when the street view photos were taken. https://www.google.

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Alan Fletcher
The roof has one circular roof fan at the left, and a rectangular box at the other. Presuming that the manufacturing area was was adjacent to JM's offices (on the left) the left-most circular fan vents the manufacturing area. Heres the fan : http://lenr.qumbu.com/steampics/160521_fans_01.jpg

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Jed Rothwell
John wrote: > Your assumption that all the power used by the customer's plant must end > up in heat in the room is not valid. A quick search of J.M Products Corp > indicates that they are in the chemicals business - wholesale and > *manufacturing*. I am not a chemist but I would guess that the

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Daniel Rocha
There isn't evidence for almost everything besides words from IH and Rossi/Lewan. But the area required for cooling is small, so I don't think that this point is a big issue. 2016-05-21 16:56 GMT-03:00 David Roberson : > Is there evidence for the existence of an input opening adequate to > achiev

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Jed Rothwell
a.ashfield wrote: > There is a difference between saying "in my opinion Rossi is a fraud" and > a statement of fact, that you have made several times. "Rossi is a fraud." Okay, let me put it this way: The evidence that he is a fraud is now overwhelming in my opinion. > For the latter you

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread David Roberson
Sent: Sat, May 21, 2016 3:29 pm Subject: Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal That's a surprisingly small volume. The machine has one of its smaller dimensions 3 meters. So, even 1.5m/s per second at one end would cool the device.

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Alan Fletcher
on. From: "Jed Rothwell" To: "vortex-l" Sent: Saturday, May 21, 2016 10:00:49 AM Subject: Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal Peter Gluck < peter.gl...@gmail.com > wrote: Jed you say you know the data

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Daniel Rocha
Why do you assume there were no tubes taking the heat through the ceiling. Even in the 10/28/2011 1MW there were. And indeed, there was a model of fan similar to the smallest model displayed on the site you gave the link. At least that I could see in the video by Mats Lewan. 2016-05-21 16:37 GM

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Alan Fletcher
uot;vortex-l" Sent: Saturday, May 21, 2016 12:29:44 PM Subject: Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal That's a surprisingly small volume. The machine has one of its smaller dimensions 3 meters. So, even 1.5m/s per second at one end would cool the device.

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Alan Fletcher
12:21:04 PM Subject: Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal Correction ... the photos on that page were lower CFM ... 36 to 42 inch diameter, not so teeny tiny. eg http://www.industrialfansdirect.com/IND-FA-EF-PM-A/LFI-ADD36T11000B.ht

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Daniel Rocha
----- > *From: *"Alan Fletcher" > *To: *"vortex-l" > *Sent: *Saturday, May 21, 2016 10:37:55 AM > *Subject: *Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without > industrial ventilation would be fatal > > This chimney sizing link doesn't

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Alan Fletcher
Correction ... the photos on that page were lower CFM ... 36 to 42 inch diameter, not so teeny tiny. eg http://www.industrialfansdirect.com/IND-FA-EF-PM-A/LFI-ADD36T11000B.html 30K CFM, 36 inch From: "Alan Fletcher" That's a teeny tiny little fan! http://www.industrialfansdirect.com/wall-v

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Alan Fletcher
rday, May 21, 2016 10:37:55 AM Subject: Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal This chimney sizing link doesn't really apply --- it's for natural draft up a chimney of a given height and diameter -- WITHOUT a fan. (The longer t

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread John
On 21/05/2016 11:13 PM, Jed Rothwell wrote: Once again people have claimed you can release 1 MW with no ill effects in a small facility, without industrial scale ventilation. People should apply some common sense metrics! Rossi says the facility is 6,500 sq. feet. Conventional heating calls

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Alan Fletcher
This chimney sizing link doesn't really apply --- it's for natural draft up a chimney of a given height and diameter -- WITHOUT a fan. (The longer the chimney the higher velocity of the draft, so a given diameter can exhaust more heat. They recommend " The velocity of air and flue gas in a sma

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread a.ashfield
Jed, If, as likely, the output of the E-Cats was not much above 100C, one would need some provision to ensure there wasn't excessive water carry over. Indeed without that the whole system might fill with liquid. Until shown otherwise I expect that was done. I also expect the steam to be wet

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread a.ashfield
Jed, There is a difference between saying "in my opinion Rossi is a fraud" and a statement of fact, that you have made several times. "Rossi is a fraud." For the latter you could be sued for libel in court.

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Jed Rothwell
Peter Gluck wrote: Jed you say you know the data but have to keep them secret. > Correct? > Rossi himself revealed some of the most important details in his interview with Lewan. His numbers show that the temperature was close to 100 deg C. With just a little pressure, a slight error in the temp

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Peter Gluck
Jed you say you know the data but have to keep them secret. Correct? Can you please tell the most 'innocent' ones- the daily consumes of electric energy from the grid by the 1MW plant? peter On Sat, May 21, 2016 at 7:16 PM, Jed Rothwell wrote: > a.ashfield wrote: > > >> Jed, I gave you one exa

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Jed Rothwell
a.ashfield wrote: > Assuming Rossi (and others) are guilty before the trial is not the > American way. > This only applies to the courts and the legal system. A citizen outside the legal system is free to decide someone is guilty or innocent. That is no violation of tradition or law. I am not a

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Jed Rothwell
a.ashfield wrote: > Jed, I gave you one example from first hand experience, that was a 1.5 > ton/day art glass furnace and someone else provided examples of 4 MW > boilers. So common sense tells me it is not unreasonable to do so. > How much power did your glass furnace consume? Was the facil

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread a.ashfield
Jed, Assuming Rossi (and others) are guilty before the trial is not the American way. Or do you prefer Napoleonic law?

Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread a.ashfield
Jed. "Once again people have claimed you can release 1 MW with no ill effects in a small facility, without industrial scale ventilation. People should apply some common sense metrics!" Jed, I gave you one example from first hand experience, that was a 1.5 ton/day art glass furnace and someone

[Vo]:1 MW of heat in a 6,500 sq. ft. facility without industrial ventilation would be fatal

2016-05-21 Thread Jed Rothwell
Once again people have claimed you can release 1 MW with no ill effects in a small facility, without industrial scale ventilation. People should apply some common sense metrics! Rossi says the facility is 6,500 sq. feet. Conventional heating calls for no more than 20 BTU/sq. ft. in Florida. That's