On 2001-08-07, Devon wrote:

>> Does anyone know how to reach the project maintainers?
>>
>> Message from  yahoo.com.
>> Unable to deliver message to the following address(es).
>> <[EMAIL PROTECTED]>:
>> Sorry, I wasn't able to establish an SMTP connection. (#4.4.1)
>
>Hrmm, that address was valid not too long ago, and is still listed on
>their web site. I used it perhaps a month ago.

I've sent the 2nd try via my own server, and it has left the queue.
The one sent via Yahoo has come back after one week.

>> Question 2:
>>
>> # rpm -q lm_sensors
>> lm_sensors-2.5.5-3
>>
>> I think the naming of "*_over" and "*_hyst" is swapped:
>>
>>     set temp1_hyst 50
>>     set temp1_over 52
>
>These are confusing, but correct, I believe. I decided this after
>having read the notes in the config file 30 or 40 times. :) An argument
>could be made either way, when you take the sensors output below into
>consideration. In this usage, for temp1, the overtemp alarm will turn
>on at 52, and off at 50.
>
>> SYS Temp: +48.3�C   (limit = +50�C, hysteresis = +52�C)
>
>I took this to mean that while 52 is the limit, to prevent oscillation
>between alarm on and off, we alarm at 52, and remain in the alarm state
>until the temp cools to 50.
>If it were handled the opposite way (limit 52, hysteresis 50), the
>alarm would remain on, after the temp had dropped below the the high
>limit. You'd see (after the alarm had triggered at 52, and we cooled a
>bit):
>SYS Temp +51C (hysteresis= +50�C, limit = +52�C) ALARM
>I'm sure there are those who would argue that we shouldn't be in an
>alarm state if the temp is below the limit.

Hmmm, let's see. I have used more clear values now to emphasize the
difference. According to this setting,

     set temp1_over 52

52�C should be the threshold which triggers alarm if the temperature
goes _OVER_ this value. And when it has cooled down thus far

     set temp1_hyst 40

alarm will be stopped again.

BUT the sensors output reports

  limit = +40�C, hysteresis = +52�C)

which is swapped. Now, a while ago someone posted this on the
Seawolf list:

  set temp_over 30
  set temp_hyst 5

  limit = +30�C, hysteresis =  +5�C

Here it is NOT swapped.