TJI has become a generic name for all web type joist, but they vary greatly in their engineering support from Mfg. to Mfg. If indeed you are using the "Truss Joist McMillan" TJI or the (Wearhouser) TJI your in luck. If its another brand such as BCI or Louisiana Pacific info is harder to get. The method we have used in the past and had approved by the TJI engineering staff is to install two pieces of plywood to reinforce the web as per their bearing point detail (Nails and Construction adhesive) then use the Sammy side winder through the plywood reinforcement to hang from this will allow your hanger to hang perpendicular or as a pendent for slope roof/ceiling structures. Please note that while TJI only requires 3/4" plywood, you'll need to use 7/8" to keep your 2" Sammy screw in the wood, and not sticking out the other side.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "Steve Leyton" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, November 14, 2006 9:59 AM
Subject: RE: Hanging off TGI's


The other consideration is that the chord stock on composite wood products is laminar and has a directional bias. Structurally, I don't know if you can even drill an angled hole in the chords - my guess is that you can't because it has little or no shear strength. Drucker's advice is excellent: either obtain a sprinkler systems guidebook from TrusJoist, or correspond with the engineering department of the manufacturer of the product you have on your project. Ask them to show you the exact detail they recommend and then run with it.

Steve Leyton
Protection Design & Consulting



-----Original Message-----
From: Jimmy Waite [mailto:[EMAIL PROTECTED]
Sent: Tuesday, November 14, 2006 8:39 AM
To: [email protected]
Subject: RE: Hanging off TGI's


Ed,
First I need to correct my self.  We typically use Hangermates, not Sammys.
Secondly, my concern with installing at an angle is that the anchor would
not be fully embedded, so the pull-out strength would not longer be valid.
My final concern is that the sheet rockers will most likely be on the job
before us, so getting into the space to use blocking would be very
difficult.

Jimmy

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: Tuesday, November 14, 2006 9:07 AM
To: [email protected]
Subject: RE: Hanging off TGI's

Jimmy, why can't you drill in at an angle?

Ed Kramer
Littleton, CO


I have come across a situation where I have to hang from TGIs that has a 4
in 12 pitch and our pipe is directly below the TGIs.  Also, the bottoms of
the joists are dry walled.  Normally when we hang from wood we would use a
Sammys.  We can't use the Sidewinder because we can't get more than 2"
from
the bottom of the joist.  Also, we can't use a regular Sammy and drill in
at
an angle (to allow the all thread rod to hang straight down).  Has anyone
else come across a similar situation, and if so, how did you address it?

I did some searching on the internet and found some hangers that have
linked
eye rods.  Has anyone seen, or had any experience with these?


Jimmy Waite
Burtell Fire Protection, Inc.
Billings, MT
[EMAIL PROTECTED]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to