Thanks guys.  The logic is there.  NFPA 13 does not allow us to eliminate
sprinklers from ele. equip rooms so logic tells me phase 1 recall is ALWAYS
required in a fully sprinklered building with an ele equip room (ASME
A17.1-2.27.3.2.1)  As for the shunt trip....ASME A17.1-2000 2.8.2.3.2 and
Florida building code 3006.5 pretty much says you need a shunt trip.  

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John Drucker
Sent: Wednesday, November 15, 2006 9:07 AM
To: [email protected]
Subject: RE: Elevator Recall


George,

Sprinklers may be omitted in the hoistway if a) hoistway is non combustible,
b) car is non combustible construction and c) Hydraulic fluids (if hydraulic
elevator) are non-combustible.  However there is no such exception for the
elevator machine room which must be sprinklered hence the need for shunt
trip due to this sprinkler.

Phase I Recall is always required, the 25ft travel rule eliminated. If
sprinklers are omitted from the hoistway due to the conditions listed above
then a smoke detector is not required and actually prohibited at the top of
the hoistway.  However  a smoke detector configured for phase I recall is
required at each lobby and the elevator machine room.

Let me know if you need the code references, I can provide them when I get
back in.

John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Geoff Dyce
Sent: Wednesday, November 15, 2006 8:57 AM
To: [email protected]
Subject: Elevator Recall

Roland or someone....I need your input re: a question put to me yesterday.
When a building has an elevator, when would an elevator recall and shunt be
required??  The building is totally sprinklered, elevator is per ASME A17.1
with no sprks at the top and bottom of the shaft.  I say always and others
say I'm wrong.  What do you say??


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to